Results 1 to 4 of 4
  1. #1
    Join Date
    Jul 2005
    Location
    Belarus
    Age
    51
    Posts
    25
    Rep Power
    0

    Hot gas defrost in commercial refrigeration



    Hello, experts
    I'm looking for information about hot gas defrost system.
    I know some theory, but never seen real system.
    It would be great to see working system photo.
    Has anyone tried an hot gas defrost system for low temperature islands, how did it work out?
    What world's manufacturers use it?
    What advantages and disadvantages hot gas defrost system in comparison electrical defrost system?
    Thanks for any advance or link.



  2. #2
    Join Date
    May 2006
    Location
    viet nam
    Age
    39
    Posts
    18
    Rep Power
    0

    Re: Hot gas defrost in commercial refrigeration

    the advantages: short time deforst ( my system is 1 minute), no danger of electric leakage, energy saving.
    the disadvantages: can make compressor head temperature high, need hot gas solenoid valve+pipe+timer+control devices depend on required design.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Hot gas defrost in commercial refrigeration

    Here's a Parker book on HG defrost for ammonia which should be useful to you...
    http://www.parker.com/RS/90-11a.pdf
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Nov 2006
    Location
    UK
    Age
    63
    Posts
    392
    Rep Power
    18

    Re: Hot gas defrost in commercial refrigeration

    Tralex
    I agree with the advantages listed however if the evaporator coil is not designed for hot gas do not use it as there is secere thermal shock on the coil which in a short time will lead to leaks. The better alternative is saturated gas of the top of the receiver, you still get quick defrost but without the thermal shock. I am presuming you are running multiple evaporators from one compressor or pack otherwise things get very complicated. If yo PM me with an email address I will send you some drawings to have a look at or take a look at the Sporlan site they have some good drawings.

    Ian

Similar Threads

  1. advanced refrigeration technology
    By Lc_shi in forum Fundamentals
    Replies: 10
    Last Post: 16-02-2011, 05:22 PM
  2. CO2 Applications on Commercial Refrigeration
    By pinoytoits in forum Fundamentals
    Replies: 1
    Last Post: 15-01-2006, 03:53 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •