Results 1 to 17 of 17
    India
    688
    air washer system with chilled water
    I am looking for some technical data on this issue. I had some charts from Flakt, but I am not sure if they are relevent now a days. The air temp ofcourse is less compared to normal air washer system
    May 2006
    India
    82
    1,013
    Re: air washer system with chilled water
    Could you please let me know as to what informations you require. Air Conditioning with air washer is very common. We had done a number of such works and have recently completed a project where temperature and humidity were both to be controlled. We had used humidifiers with chilled water.
    India
    688
    I am looking for charts which show air conditions after chilled water air washer against normal water ( Ambient) air washer system
    Mar 2007
    India
    38
    Insignificant, practically.
    Dec 2004
    82
    14
    Hola !
    Please be more specific on the information you
    want.
    Are you trying to design an air washer to control
    temperature and humidity while using a chilled water coil ?
    Do you want to know what happens to the air
    when passing through the washer and the coil ?
    Victorman
    India
    688
    I al looking for a situation wherein when air passes over chiiled waer air washer, at what conditions air comes out
    Nov 2005
    kankroli
    30
    I am also looking forward for the same arrangement that is using chilled water in air washer instead of normal fresh water. Has anybody idea about it? Please reply as it will help me too.
    Dec 2004
    82
    14
    Hola !
    The Trane Company in La Crosse Wisconsin USA , publishes a book titled " Trane Air Conditioning Manual ",
    this book explains in detail the action of the air and water when brought in contact with each other ,it
    also has a section on " Air Washers ".
    You can find the book in Amazon.
    l hope this will help you.
    best regards
    Victorman
    India
    688
    Many thanks Victorman
    Oct 2005
    IRAN
    878
    Hi smpsmp45,
    To know this you have to study "Mass Transfer".
    Using chilled water in an air washer is a waste of energy.
    Mohamed Khamis can help you a lot on this subject.
    Even Einstein Asked Questions
    India
    688
    I think I should send a PMS to Mr. Mohamed Khamis on this then. SOme customers do insist on this.
    May 2006
    India
    82
    1,013
    Please let us know as to the result of your discussions.
    India
    688
    Surely. I shall post that data here
    Mar 2007
    India
    38
    The effect is insignificant because of the large difference between the latent heat and sensible heat, incase of water. The latent heat of evaporation of water is about 2441.68kJ/kg (at ambient temperature) and the specific heat is 4.18kJ/kgC. This means, you have to have a temperature difference of 584 C or you have to provide 584 kgs of water, for a temperature difference of 1C if you want to remove as much heat as it is possible if you evaporate 1kg of water.
    I am giving here a sample calculation to illustrate the advantage of going with chilled water at 5C when compared to 25C water.
    Let us assume that your inlet conditions are 30C DBT and 60% RH. This corresponds to a WBT of 22.5C. Assuming 75% effectiveness of a direct evaporative cooler, you can get a dT of (30-22.5)*0.75 = 5.625C. So, you can reduce the air temperature to 24.4C. The total sensible heat removed from air can be calculated by 1.23W/(L.s.K)xflowrate(L/s)xdT(K). Assuming an air flowrate of 472L/s, the sensible heat removed form air (which is imparted to the evaporating water) equals 1.23x472x5.625 = 3265.65W (or 3.265kW). The enthalpy of water and steam at 25C are 104.83kJ/kg and 2546.5kJ/kg respectively, so the latent heat of evaporation is (2546.6-104.83) = 2441kJ/kg.
    To remove 3.265 kW from air, you have to evaporate 3.265/2441 = 0.00133kg/s of water. This is, essentially, the flowrate of water across the evaporative cooler. If you use 5C chilled water instead of using 25C water, you can get a sensible heat benefit from chilled water to the tune of 0.00133kg/s x 4.18kJ/kgC x (25-5)C = 0.11kW.
    Going back to the sensible heat equation of air, 0.11kW would reduce the air temperature by 110W/(1.23W/L.s.Kx475L/s) = 0.188C (or K).
    Hope this clarifies the issue at hand.
    India
    688
    Great explaination with example. Many thanks
    Mar 2006
    Malaysia
    48
    233
    Hi SmpSmp45
    Sorry for being late to particpate ur thread. Anyhow there is attachment I wish it could help and reply ur question.
    Best wishes
    Attached Files Attached Files
    India
    688
    Excellent info & many thanks
  1. pure water from air
    Last Post: 26-02-2009, 12:25 PM
  2. Chilled Water A/C System.. antifreeze or no?
    By WangFu in forum Technical Speculations
    Last Post: 09-08-2007, 10:36 AM
  3. Inhibitor for Chilled Water system
    By Electrocoolman in forum Air Conditioning
    Last Post: 24-06-2007, 10:53 AM
  4. Building a wine cabinet
  5. chilled water PHE
    By priti in forum Trouble Shooting
    Last Post: 31-07-2002, 08:25 PM