    Question centrifugal chillers york



    I,m working with a 360 ton centrifugal chiller and im having trouble determing if its low on refrigerant charge.This chiller uses Refrigerant 134-a.I am not sure what is the correct operating superheat or subcooling of this unit.Can someone tell me what is the best and most reliable method to determine if this unit is fully charged If you guys need anymore information on the chillers operating data to help me solve my problem just let me know.I really need to know if the chillers working correctly and efficiently.



  2. #2
    Join Date
    Apr 2006
    Location
    uae
    Age
    45
    Posts
    20
    Rep Power
    0

    Re: centrifugal chillers york

    sir,

    check unit manual or name plate. it shows how much you need to charge.

    regards,.

  3. #3
    Join Date
    Feb 2004
    Location
    USA
    Posts
    132
    Rep Power
    0

    Re: centrifugal chillers york

    The nameplates are an estimate, not even close in many instances.
    Quote Originally Posted by joel View Post
    sir,

    check unit manual or name plate. it shows how much you need to charge.

    regards,.

  4. #4
    Join Date
    Apr 2006
    Location
    uae
    Age
    45
    Posts
    20
    Rep Power
    0

    Re: centrifugal chillers york

    Quote Originally Posted by absrbrtek View Post
    The nameplates are an estimate, not even close in many instances.
    sir,
    superheat required is 1- 2 deg.F...
    pls...consider checking your...
    cooler/cond flow and approach.


    regards

  5. #5
    Join Date
    Mar 2007
    Location
    England
    Age
    57
    Posts
    15
    Rep Power
    0

    Re: centrifugal chillers york

    Hi Magic.

    would check refrigerant level in sight glass on evaporator, check delta t across evap and cond, and check operating pressures for your application,

  6. #6
    onquin's Avatar
    onquin Guest

    Re: centrifugal chillers york

    is there liquid refrigerant valve actuator installed in your unit?try to check its operation,eventhough you are having the correct amount of refrigerant in the system,calibration and proper operation of that valve and level sensor is required,

  7. #7
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: centrifugal chillers york

    measured the evaporator at 100 % capacity between the output of water and saturated evaporator temperature performance should be of 2 ° f.
    Best regards

Similar Threads

  1. Big Centrifugal chillers
    By 404cab in forum Industrial Compressors
    Replies: 49
    Last Post: 17-12-2007, 08:06 PM
  2. york gs/ gsi chillers
    By GHAZ in forum Technical Discussions
    Replies: 1
    Last Post: 16-09-2007, 10:42 PM
  3. York Centrifugal
    By Peter_1 in forum Industrial Compressors
    Replies: 12
    Last Post: 14-08-2005, 01:25 PM
  4. Centrifugal chillers part 2
    By reggie in forum Industrial Compressors
    Replies: 0
    Last Post: 16-05-2002, 09:07 AM
  5. Centrifugal chillers
    By reggie in forum Industrial Compressors
    Replies: 2
    Last Post: 02-05-2002, 07:22 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •