    Tube pitch squared/staggered



    Hi all,

    Does anybody knows why the tube pitch for ammonia evaporators use to be squared instead of staggered ( as for *****s)?

    P.D. I think that the efficiency of the fin is bigger when is staggered, because it creates a bigger turbulence in the air ...



  2. #2
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,632
    Rep Power
    24
    Hi, Friobernal
    please enlighten us on chiller construction, with regards to what tube pitch is and where the finning would be.
    Regards. Andy.

  3. #3
    Join Date
    Mar 2002
    Location
    Spain
    Posts
    67
    Rep Power
    23
    Hi Andy;

    "Tube pitch" is an expresion i have read Idonotwhere, but i mean the geometry of the tubes in an air coil evaporator, that for *****s are always staggered, and for ammonia´s coils are squared, being the fin less efficient.

    I´ve being thinking that a possible reason could be the higher K, and more frosting....

    Regards (Again)

  4. #4
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    510
    Rep Power
    24
    The Prof would think of tube pitch to be its degree of slope, which would have some implications with the suction line, but not the evaporator. By chance are you referring to how the tubes in the coil are circuited, e.g., counter-flow? Most ammonia coils are designed and used for recirc duty instead of DX, and there are some issues ergarding coil circuiting for each.
    Prof Sporlan

  5. #5
    Join Date
    Mar 2002
    Location
    Spain
    Posts
    67
    Rep Power
    23
    Let me see if i could explain it better in my poor english:
    The geometry i´m talking about, you can see in:
    http://www.ari.org/std/individual/410-2001.pdf
    (page 4) Staggered tubes and parallel (in line) tubes

    I´m attaching a brochure of a european manufacturer, where you can see (page 2) differents tubes arrangements, and for ammonia; in-line geometry is prefered.

    I know (from a book) that the compactness of staggered is a 16% higher than parallel tubes, so we obtain less efficiency....
    why using in-line instead staggered????




    Thanks for all Prof and Andy

  6. #6
    Join Date
    Mar 2002
    Location
    Spain
    Posts
    67
    Rep Power
    23
    Sorry, I cannot to attach.

    http://www.guentner-online.de/guentn...cs/pdf/gco.pdf

    Regards

  7. #7
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,632
    Rep Power
    24
    Hi, Friobernal
    the professor is correct, I was thinking about water chilling, thats what I get for working on a burst chiller all last week. The inline holes is just as the Professor says for Pumped or Flooded circulation.
    On DX or LPR NH3 (Low Pressure Recevier a bit like DX only the suction from the cooler has liquid in it) the tubes are in slope type formations, the liquid having to make a number of passes (usually 2-4) before it is boiled off, this is the same as DX ***** coolers.
    The square or in line passes are in pump circ or flooded coolers were the liquid enters the suction to be separated else where.

    Remember the only coolers which are sloped pitch that have liquid leaving them not dry gas are on LPR systems, which is a modified DX system anyways.
    Hope this helps Regards. Andy.

  8. #8
    Join Date
    Jan 2002
    Location
    Canada
    Posts
    35
    Rep Power
    0
    Originally posted by Friobernal

    "Tube pitch" is an expresion i have read Idonotwhere, but i mean the geometry of the tubes in an air coil evaporator, that for *****s are always staggered, and for ammonia´s coils are squared, being the fin less efficient.
    Hi Friobernal,

    With ammonia coil we work with carboned steel, stainless, aluminium tubing and aluminiun fins the efficiency is poored compare with cooper tubing, therefore defrost is more difficult. At low temperature (below freezing) flat fin as better result in defrost and in fouling factor efficiency than staggered.

    We just encountered a problem this summer the manufacture as supplied us straggered aluminiun fins with carboned steel tubing,and the defrost cycle was terrible. We change the coil with flat fins and no more problem. Our range of temperature was of 40dF (4.4dC) entering and 27dF (-2.8dC) leaving air.

    truly yours

    Kathleen
    Kathleen, P.eng
    www.refri-ozone.com

  9. #9
    Join Date
    Mar 2002
    Location
    Spain
    Posts
    67
    Rep Power
    23
    hi Kathleen

    What do you mean with "and the defrost cycle was terrible"?

    Does terrible mean long?

    Thanks all and regards

  10. #10
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,632
    Rep Power
    24
    Hi, Friobernal
    yes I would say that is what Kathleen means.
    Another reason for the square pitch would be cost and size, the square pitch is simplier to make and with NH3 the cooler will have smaller diamentions for a given kW capacity, so the size issue may not come into it, just the cost.
    As I stated earlier on Low Pressure Receiver Systems we use the sloped pitch, with no defrost problems, defrost problems will be associated with the fin spacing, if you had close finning and a slope pitched tube arrangement the evaporator would not be correct for low temperature work, but more than adequate for high or possibly medium temperature duty.
    Hope this helps, Regards. Andy.

  11. #11
    Join Date
    Jan 2002
    Location
    Canada
    Posts
    35
    Rep Power
    0
    Originally posted by Friobernal
    Does terrible mean long?
    Friobernal,

    time between each defrost was short because the effeciency of the coil drop from the moment that ice started to built on it.

    Defrost was also long.

    We had to defrost every 45 minutes to keep efficiency, and air flow.

    Kathleen
    Kathleen, P.eng
    www.refri-ozone.com

Similar Threads

  1. oxidation scale in copper tube and fittings
    By DeB in forum Fundamentals
    Replies: 8
    Last Post: 23-06-2006, 09:45 PM
  2. metric capillary tube
    By tralex in forum Fundamentals
    Replies: 5
    Last Post: 21-02-2006, 07:57 AM
  3. The amazing Mr. Cap Tube
    By shogun7 in forum Domestic
    Replies: 52
    Last Post: 07-01-2006, 08:33 PM
  4. Tube staggered/squared
    By bersaga in forum Fundamentals
    Replies: 2
    Last Post: 06-01-2003, 12:56 AM
  5. coaxial (tube in tube) heat exc.
    By aliugur in forum Fundamentals
    Replies: 0
    Last Post: 04-06-2002, 08:23 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •