    Floor insulation



    For atypicaal large coldroom, operating at 0degC, with a raised floor (concrete slab below)- I would ensure that the floor in insulated.

    (Besides the higher heat gain)

    Questions
    a) Is there a method to calculate the desire thickness of polyurethane insulation floor panels?
    b) Is ther a formula I could use to calculate if condensation would form. (Ambient temperature belwo the floor would be typically 25oC)

    Thanks



  2. #2
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: Floor insulation

    Typcailly the floor insulation thickness should be as that of walls. If you are using PUF then for your application 80mm thk is good enough. Ahsrae gives a formula for minimum R value of the insulation. Infact I had posted that table in one of the querries.

  3. #3
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: Floor insulation

    I can not attcah that file. But that you can find it Sandwich panel thread
    Last edited by smpsmp45; 18-09-2007 at 04:29 PM. Reason: file did not go through

  4. #4
    Join Date
    Jun 2007
    Location
    South Africa
    Posts
    80
    Rep Power
    17

    Re: Floor insulation

    Thank - will search for the sandwich panel thread