For atypicaal large coldroom, operating at 0degC, with a raised floor (concrete slab below)- I would ensure that the floor in insulated.
(Besides the higher heat gain)
Questions
a) Is there a method to calculate the desire thickness of polyurethane insulation floor panels?
b) Is ther a formula I could use to calculate if condensation would form. (Ambient temperature belwo the floor would be typically 25oC)
Thanks
-
18-09-2007, 04:09 PM #2
Re: Floor insulation
Typcailly the floor insulation thickness should be as that of walls. If you are using PUF then for your application 80mm thk is good enough. Ahsrae gives a formula for minimum R value of the insulation. Infact I had posted that table in one of the querries.
-
18-09-2007, 04:28 PM #3
Re: Floor insulation
I can not attcah that file. But that you can find it Sandwich panel thread
Last edited by smpsmp45; 18-09-2007 at 04:29 PM. Reason: file did not go through
-
18-09-2007, 04:48 PM #4
Re: Floor insulation
Thank - will search for the sandwich panel thread