    cold room temp & the product temp



    It is a well known fact that the cold rom temp is generaly the return air temp on the evap coil. many a times the client gets worried when the door is opened & the temp almost imediately shoots up. Though the product temp is unchanged, he is always worried.
    Is there any technical literature explaining this phenomenon?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: cold room temp & the product temp

    The air temperature will always rise when a door is opened and external air is allowed inside.

    The product temperature will remain more constant because of its mass.

    Try changing the temperature probe from an 'air' sensor to a 'product' sensor or improve the the door seal arrangements to reduce the effect of door openings.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: cold room temp & the product temp

    Another option is to put the sensor for an elextronic thermometer in a 500ml bottle filled with glycol mixture (screwed to the wall).

    When the customer looks at the thermometer, he will see the "mean" room temperature wich will be close to the temperature of the products in the room.

  4. #4
    Join Date
    May 2007
    Location
    India
    Posts
    695
    Rep Power
    17

    Re: cold room temp & the product temp

    Dear Viking,

    Seems to be the practical suggestion. We can surely use that in our new projects.

  5. #5
    Join Date
    Mar 2004
    Location
    UK
    Posts
    625
    Rep Power
    21

    Re: cold room temp & the product temp

    Hi

    If its for future projects then look at your choice of controller.You could opt for a controller that controls the temp on return air but displays a % off Air on /Air off giving a more stable display temp.Or leave the the digital display inside the the controll panel and fit a box guage.

    However if the customer is leaving the door open to long then your just masking the problem,it might be better to fit an annoying door alarm that activates after 60 secs.They,ll soon close the door.

    Regards Bernard

  6. #6
    Join Date
    Aug 2007
    Location
    Malawi
    Age
    40
    Posts
    19
    Rep Power
    0

    Re: cold room temp & the product temp

    thats a good idea,

  7. #7
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: cold room temp & the product temp

    or put a micro switch on the door so it stops the fans and pumps the unit down,with the probes being on or arround the blower they should stop stable untill the door is closed,but then they should expect it to go up a bit. this helps with icing up problems on freezers but if its a chiller i would go with the slow acting probe or the vessel with fluid in.

  8. #8
    Join Date
    Sep 2007
    Location
    New Zealand
    Age
    79
    Posts
    54
    Rep Power
    17

    Re: cold room temp & the product temp

    Hi smpsmp45.
    If you can check out ASHRAE Refrigeration Hand Book Chapter 12 " Infiltration Air Loads" , gives a good insight in to the effect of Warm Air flowing in to Freezer rooms. Frost accumulation and the formation of ice crystals can be a more adverse effect that product temperature rise.

  9. #9
    Join Date
    May 2007
    Location
    India
    Posts
    695
    Rep Power
    17

    Re: cold room temp & the product temp

    Dear John,

    Many thanks

  10. #10
    Join Date
    Sep 2006
    Location
    Venezuela
    Posts
    259
    Rep Power
    18

    Re: cold room temp & the product temp

    Hi smpsmp45

    The room tempertaure is formed for a 3D set of isotermal curves . The lowest temperature is leaving the evaporator and the highest is in the return (inlet of the evaporator). When you open a door this pattern changes and the highest temperature could be close to the door. A new isotermal pattern is formed. Normally the product has an inertial temperature constant that depend of many factor incluiding the enclousure. So the poduct do not react so fast to the temperature changes.It is a logarism aproch
    If you instal a electronic temperatur sensor far from the door and in the return side of the farer evaporator It may help to have a better idea of the temperature.
    You also could install hawain plastic courtain or even fast acting door together with horizontal openning door see www.ritehite.com

Similar Threads

  1. Cold Room Design - minus 25deg C
    By vijay_study in forum Fundamentals
    Replies: 34
    Last Post: 11-11-2009, 08:12 AM
  2. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  3. Compressor suction icing up on cold room set up
    By Leviathan in forum Trouble Shooting
    Replies: 9
    Last Post: 02-06-2007, 05:08 AM
  4. LG Capacitor - Room not cold
    By kelamel in forum Trouble Shooting
    Replies: 8
    Last Post: 21-10-2006, 10:50 AM
  5. Installation of cold room
    By Josip in forum Legal-Business-Marketing
    Replies: 12
    Last Post: 12-03-2006, 10:20 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •