    Angry Locating air cooled condenser on the roof or on the ground?



    Hi,

    What would be your advice or opinion as to the preferred location of air cooled condensers. We may put them on the roof of the building (21 Ft (7 m) high). I am reluctant because of the difficult access in cases of maintenance and breakdowns. Plus we have snow and ice in the winter ... On the other hand, they are out of the way...

    On the ground, they are accessible, but more vulnerable. They'd have to mounted on high enough frames to clear the snow ...

    Any considerations I am not factoring in ...?

    Thanks,



  2. #2
    Join Date
    Apr 2007
    Location
    SOUTHAFRICA
    Age
    43
    Posts
    26
    Rep Power
    0

    Re: Locating air cooled condenser on the roof or on the ground?

    here in sa i would go with placing them on the roof do to theft but also to keep it away from anything like dust and paper getting caught behind it and cause it to under condence ,if in your case if i place it on the roof i would fit fan speed controllers to the condencer fans to prevent over condencing in winter,cheers

  3. #3
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Locating air cooled condenser on the roof or on the ground?

    Measures can be taken to prefent damage or theft when the condensor is at ground level.

    The best reason to choose either option would be pipe run. The shorter the distance , the better in terms off charge.

    How ever, if the condensor is below the compressor, this is not always a good solution and can give many problems later on in terms of oil return.

    If the roof is the only option, the customer will have to make provisions to get roof acces in a safe way and a correct way so you can bring tools and/ or spares to it!

  4. #4
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Locating air cooled condenser on the roof or on the ground?

    Quote Originally Posted by halacoque View Post
    Hi,


    Any considerations I am not factoring in ...?

    Thanks,
    My choice would be to put it high on the roof.
    If you have to make a frame for it to sit higher than the snow then for the same cost or not much more you could make an access ladder and gantree for safe access to the roof all year round.

    Cheers taz.

  5. #5
    halacoque's Avatar
    halacoque Guest

    Thumbs up Re: Locating air cooled condenser on the roof or on the ground?

    Thank you for your kind assistance and expertise. I will locate the condensers on the roof or sufficiently elevated from the ground and snow level to have a good air flow while maintaining the condensers above the HP receivers.

    Thanks again.

Similar Threads

  1. method to design air cooled condenser
    By abbasi in forum New Technologies
    Replies: 4
    Last Post: 12-02-2008, 08:34 AM
  2. Making a simple water cooled condenser
    By The MG Pony in forum Fundamentals
    Replies: 19
    Last Post: 01-08-2007, 11:02 AM
  3. How to adjust head on a water cooled condenser
    By kengineering in forum Technical Speculations
    Replies: 5
    Last Post: 30-05-2007, 10:37 PM
  4. water cooled condenser shell type
    By abbasi in forum New Technologies
    Replies: 0
    Last Post: 27-04-2005, 08:32 AM
  5. air cooled condenser design
    By abbasi in forum Fundamentals
    Replies: 1
    Last Post: 26-03-2005, 08:33 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •