    how to sizes the blower and condenser for a freezer



    hi, i am new in refrigeration system. Now i have cold room sizes is 14' x 12' x 8'h. i will using copeland scroll ZR81kc-TFD-522 7.0hp R22 compressor. Total is 6.6kw at -23deg c. how should i sizes my condenser and blower. Please advise me.



  2. #2
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: how to sizes the blower and condenser for a freezer

    Mate basically you should size the evaporator first for the heat load on the room. Then select a compressor to do that duty and finally a condenser that will reject both the comp capacity and also the heat added during compression - you can just add the input power to the comps capacity to come up with a total heat to be rejected - this is your condenser capacity. For a freezer you will need to consider pulldown off defrost, I like a bit more KW up my sleeve for pulldown and maybe an unloader for low loads (depends on your customer and the $$$ I suppose)

    Oh and R22 is not the best gas for low temp, you would be heaps better off using r404a or r507

    If you are hell bent on using that scroll then select an evap to do same or slightly less kw - if comp does 6.6kw then anything from 6.0 to 6.6 kw will do for the evap at say -30 SST at a 7K td (you said -23 I assume thats room temp). For the condenser add the input power to the 6.6kw to come up with a total. Select a condenser based on say a 40C ambient (or the max you will see in your region) and a nice low TD like say 8k or even lower if you must use r22, so on a 40C day you will run 48C SCT
    Last edited by 750 Valve; 17-09-2007 at 02:00 PM. Reason: coz i can
    ...and she said "give it to me you big fridgie"

  3. #3
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: how to sizes the blower and condenser for a freezer

    As per Select6 of Copeland Software, the size of the condenser should be 10.35 kw. Once you have finalised the compressor capacity, you should find the Total Heat Rejection which is the Condenser size. The Cooling Load you will have to size as per the compressor capacity, the application etc.

  4. #4
    Join Date
    Aug 2007
    Location
    MALAYSIA
    Age
    44
    Posts
    6
    Rep Power
    0

    Re: how to sizes the blower and condenser for a freezer

    hi. anyone can tech me sizing evaporator for a coldroom

  5. #5
    Join Date
    May 2007
    Location
    minnesota
    Posts
    8
    Rep Power
    0

    Re: how to sizes the blower and condenser for a freezer

    Quote Originally Posted by irwinchong80 View Post
    hi, i am new in refrigeration system. Now i have cold room sizes is 14' x 12' x 8'h. i will using copeland scroll ZR81kc-TFD-522 7.0hp R22 compressor. Total is 6.6kw at -23deg c. how should i sizes my condenser and blower. Please advise me.
    Make sure you have the correct btu rating of the condensing unit and make sure you match the btu rating to the evaporator btus. Do not use horsepower of the compressor as your determing factor but, btus.

Similar Threads

  1. Replies: 11
    Last Post: 22-07-2007, 10:38 AM
  2. Bush/Camp freezer
    By FNQ Bunyip in forum Technical Discussions
    Replies: 3
    Last Post: 24-07-2005, 02:35 PM
  3. Integral cabinet condenser cleaner
    By Mark in forum Supermarket Refrigeration
    Replies: 0
    Last Post: 05-04-2004, 05:14 PM
  4. Condenser Blower
    By Abe in forum Tools and Calculators
    Replies: 11
    Last Post: 30-01-2004, 09:59 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •