Results 1 to 5 of 5
-
17-09-2007, 10:06 AM #1
how to sizes the blower and condenser for a freezer
hi, i am new in refrigeration system. Now i have cold room sizes is 14' x 12' x 8'h. i will using copeland scroll ZR81kc-TFD-522 7.0hp R22 compressor. Total is 6.6kw at -23deg c. how should i sizes my condenser and blower. Please advise me.
-
17-09-2007, 01:51 PM #2
Re: how to sizes the blower and condenser for a freezer
Mate basically you should size the evaporator first for the heat load on the room. Then select a compressor to do that duty and finally a condenser that will reject both the comp capacity and also the heat added during compression - you can just add the input power to the comps capacity to come up with a total heat to be rejected - this is your condenser capacity. For a freezer you will need to consider pulldown off defrost, I like a bit more KW up my sleeve for pulldown and maybe an unloader for low loads (depends on your customer and the $$$ I suppose)
Oh and R22 is not the best gas for low temp, you would be heaps better off using r404a or r507
If you are hell bent on using that scroll then select an evap to do same or slightly less kw - if comp does 6.6kw then anything from 6.0 to 6.6 kw will do for the evap at say -30 SST at a 7K td (you said -23 I assume thats room temp). For the condenser add the input power to the 6.6kw to come up with a total. Select a condenser based on say a 40C ambient (or the max you will see in your region) and a nice low TD like say 8k or even lower if you must use r22, so on a 40C day you will run 48C SCTLast edited by 750 Valve; 17-09-2007 at 02:00 PM. Reason: coz i can
...and she said "give it to me you big fridgie"
-
17-09-2007, 06:06 PM #3
Re: how to sizes the blower and condenser for a freezer
As per Select6 of Copeland Software, the size of the condenser should be 10.35 kw. Once you have finalised the compressor capacity, you should find the Total Heat Rejection which is the Condenser size. The Cooling Load you will have to size as per the compressor capacity, the application etc.
-
26-09-2007, 03:08 AM #4
Re: how to sizes the blower and condenser for a freezer
hi. anyone can tech me sizing evaporator for a coldroom
-
26-09-2007, 05:29 AM #5
Similar Threads
-
How does an inverter fan coil communicate with its condenser?
By kevin090972 in forum Heat PumpsReplies: 11Last Post: 22-07-2007, 10:38 AM -
Bush/Camp freezer
By FNQ Bunyip in forum Technical DiscussionsReplies: 3Last Post: 24-07-2005, 02:35 PM -
Integral cabinet condenser cleaner
By Mark in forum Supermarket RefrigerationReplies: 0Last Post: 05-04-2004, 05:14 PM -
Condenser Blower
By Abe in forum Tools and CalculatorsReplies: 11Last Post: 30-01-2004, 09:59 PM