    Comms Problem



    Hi Guys,

    2 Fujitsu ceiling cassettes, 2 outdoor units.

    Problem..... 2 cassettes, 1 controller, Master- Slave situation.

    Master works fine slave doesn't comunicate with outdoor unit.
    As far as i am aware the controller is wired correctly, wires 1,2,3 in master and 2,3 in slave. Units identified as 0 in master and 1 in slave.

    2 outdoor units identical and have swapped everything but no joy so problem must be in ceiling cassette.

    Any ideas ??????



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Comms Problem

    The cassettes don't communicate with the outdoor units via the controller - they communicate via the indoor/outdoor wiring.

    What's the problem - what does it not do???

  3. #3
    Join Date
    Jul 2007
    Location
    staffordshire
    Posts
    22
    Rep Power
    0

    Re: Comms Problem

    Sorry Frank had a long weekend.

    The problem is that when you switch the system on both indoor units switch on but only 1 outdoor works, so the slave unit not communicating with its own outdoor unit.

  4. #4
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: Comms Problem

    or could it be a fault on the outdoor unit? a safty maybe
    ? try running the "slave" unit with the controller as a one on one unit,are you getting any fault codes?
    Paul


    "KEEP IT COOL"

  5. #5
    Join Date
    Feb 2005
    Location
    Aberdeen
    Age
    48
    Posts
    168
    Rep Power
    20

    Re: Comms Problem

    Hi can you use a volt meter and fault finding techniques to source your problem. also make sure you have programmed the controller for 2 units...!!!

    Regards Jase

  6. #6
    Join Date
    Jun 2007
    Location
    northampton
    Age
    43
    Posts
    5
    Rep Power
    0

    Re: Comms Problem

    Check the link wire, does it have a isolator? How quickly does the error show after isolation? Problem may be caused by user. All to often the case!

  7. #7
    Join Date
    Jul 2007
    Location
    staffordshire
    Posts
    22
    Rep Power
    0

    Re: Comms Problem

    Hi Guys,
    Thanks for your thoughts but hopefully I sorted it today, after swapping nearly every pcb and parts on the units.

    What was causing the problem was that a tank pump was fitted to the side of the slave unit and when it kicked in to pump the water away it stopped the outdoor unit working?? Haven't got a clue why but gave the pump its own power source instead of connecting to the cassette and now everthing works fine..........fingers crossed

  8. #8
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: Comms Problem

    Quote Originally Posted by aza View Post
    Hi Guys,
    Thanks for your thoughts but hopefully I sorted it today, after swapping nearly every pcb and parts on the units.

    What was causing the problem was that a tank pump was fitted to the side of the slave unit and when it kicked in to pump the water away it stopped the outdoor unit working?? Haven't got a clue why but gave the pump its own power source instead of connecting to the cassette and now everthing works fine..........fingers crossed
    was the pump high level wired thought the comms cable?
    Paul


    "KEEP IT COOL"

  9. #9
    Join Date
    Feb 2007
    Location
    oldham
    Age
    49
    Posts
    44
    Rep Power
    0

    Re: Comms Problem

    Quote Originally Posted by superswill View Post
    was the pump high level wired thought the comms cable?
    you should always give the tank pump its own power source.

  10. #10
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: Comms Problem

    Quote Originally Posted by fazzamouse View Post
    you should always give the tank pump its own power source.

    sorry my post was vage,by high level i was meaning the high level safty switch of the externaltank pump wired thought the comms cable of the indoor as opposed to the 240v power for the pump

    http://www.jupiterheating.com/little...ages/vcmaL.jpg
    Paul


    "KEEP IT COOL"

  11. #11
    Join Date
    Jul 2007
    Location
    staffordshire
    Posts
    22
    Rep Power
    0

    Re: Comms Problem

    Hi, whoever installed this system wired the pump to the power cable inside the indoor unit which comes from the outdoor which also acts as the comms cable.

    Can i just say this is a great site and thanks to all who help out we lesser mortals with problems....cheers.

  12. #12
    Join Date
    Feb 2005
    Location
    Australia
    Posts
    123
    Rep Power
    21

    Re: Comms Problem

    The biggest thing to remember is that inside a Fujitsu unit a RED wire IS NOT AN ACTIVE!!!. On the cassettes and inverters and anything that uses 3 wire interconnects with a controller pcb in the outdoor unit uses the following colour code inside the unit

    RED = Comms, signal wire
    WHITE = Neutral
    BLACK = Line (Active)

    It is not unheard of for things like pumps or damper motors that are connected to indoor unit terminals to cause communication issues between indoor and outdoor units. As the comms wire uses the Neutral as it's reference using the top and bottom half of an AC sinewave to send info in each direction. Any interference from those things can upset the communication.

    Can you explain exactly how it was wired and what model the cassettes were? I will have a look at some wiring diagrams and try and explain what was going on for you. Was it the power supply to the pump or a set of high level alarm contacts, that was wired to the indoor unit and to which terminal?

    With the multiple sets of units from one controller there are also dip switch settings on the wall controller when multiple systems are connected.
    Last edited by ozairman; 19-09-2007 at 06:07 PM. Reason: White was hard to see

  13. #13
    Join Date
    Jul 2007
    Location
    staffordshire
    Posts
    22
    Rep Power
    0

    Re: Comms Problem

    Hi ozairman,

    The Aspen Tank pump power cable was wired into the same terminals that you connect the cable from the indoor unit to the outdoor unit.

    Model AUY25RCZL or RZCL

    The switches on the controller were ok.

Similar Threads

  1. A strange problem
    By MuhengineeR in forum Air Conditioning
    Replies: 14
    Last Post: 27-10-2010, 05:21 PM
  2. York Screw Oil Problem
    By tomt in forum Technical Discussions
    Replies: 10
    Last Post: 02-12-2009, 02:48 PM
  3. Oil carry over Problem in Refrigeration Unit
    By imranmd in forum Industrial
    Replies: 1
    Last Post: 27-08-2007, 03:09 PM
  4. Hot start problem on VRV REYQ14M7W1B
    By cool#9 in forum Air Conditioning
    Replies: 9
    Last Post: 20-04-2007, 08:09 PM
  5. LG 10.5 kw cassette timer problem
    By Andy W in forum Air Conditioning
    Replies: 10
    Last Post: 25-06-2005, 07:09 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •