    Air cooled chillers vibration isolation



    Hi,

    We are into process of procuring 300TR x 6 Nos. air cooled chillers for one of our R&D centers.

    The chillers are located on the terrace of the R & D center alongwith the pumps.

    What is the vibration frequency range for chillers in general?

    Ways and means to reduce vibration tranmission chillers to the structure?

    Please guide.

    Regards

    Vijay Kumar


    Vijay Kumar
    HVAC Design Engineer

    BMCPL

    "The more you sweat in peace less you bleed in war"

  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Air cooled chillers vibration isolation

    Anti vibration feets under the chiller (normally, on heavier plant, these would be an enclosed spring with bolt holes above and below) and flexible pipe and/or joints in the pipework.
    Last edited by The Viking; 16-09-2007 at 06:29 PM.

  3. #3
    Join Date
    Feb 2009
    Location
    dehli
    Age
    53
    Posts
    6
    Rep Power
    0

    Re: Air cooled chillers vibration isolation

    first of all you check the pump alignment check if your pump alignmentis not ok than vibration occour due to dis ailgnment .and you also vibration pad use in pump frame base.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Air cooled chillers vibration isolation

    ^^ I think that you should perhaps check the dates before you reply.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. Frick RTM120SEB8 vibration concern
    By evapcoil in forum Industrial Compressors
    Replies: 13
    Last Post: 29-07-2009, 08:15 AM
  2. Replies: 9
    Last Post: 30-01-2009, 07:50 AM
  3. Luiquid line vibration and liquid hammer
    By Infinity in forum Trouble Shooting
    Replies: 12
    Last Post: 09-02-2007, 10:22 PM
  4. Mcquay PES Flooded Water Cooled Screw Chiller
    By Brian in forum Technical Speculations
    Replies: 4
    Last Post: 05-07-2006, 09:43 PM
  5. Liquid Chillers
    By elmusasc in forum Industrial
    Replies: 2
    Last Post: 18-05-2006, 11:06 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •