16-09-2007, 01:00 PM #1
Air cooled chillers vibration isolation
We are into process of procuring 300TR x 6 Nos. air cooled chillers for one of our R&D centers.
The chillers are located on the terrace of the R & D center alongwith the pumps.
What is the vibration frequency range for chillers in general?
Ways and means to reduce vibration tranmission chillers to the structure?
Please guide.
Vijay Kumar
Vijay Kumar
HVAC Design Engineer
BMCPL
"The more you sweat in peace less you bleed in war"
16-09-2007, 06:19 PM #2
Re: Air cooled chillers vibration isolation
Anti vibration feets under the chiller (normally, on heavier plant, these would be an enclosed spring with bolt holes above and below) and flexible pipe and/or joints in the pipework.
06-10-2009, 02:36 PM #3
first of all you check the pump alignment check if your pump alignmentis not ok than vibration occour due to dis ailgnment .and you also vibration pad use in pump frame base.
06-10-2009, 08:53 PM #4
^^ I think that you should perhaps check the dates before you reply.
Frick RTM120SEB8 vibration concern
By evapcoil in forum Industrial CompressorsReplies: 13Last Post: 29-07-2009, 08:15 AM -
EC and Air cooled condensers working in parallel
By Josip in forum NH3Replies: 9Last Post: 30-01-2009, 07:50 AM -
Luiquid line vibration and liquid hammer
By Infinity in forum Trouble ShootingReplies: 12Last Post: 09-02-2007, 10:22 PM -
Mcquay PES Flooded Water Cooled Screw Chiller
By Brian in forum Technical SpeculationsReplies: 4Last Post: 05-07-2006, 09:43 PM -
Liquid Chillers
By elmusasc in forum IndustrialReplies: 2Last Post: 18-05-2006, 11:06 PM