    ice removal from evaporator coils



    Many a times , there is large ice built up on evaporator coils. We tried various means like water spray, use of blow torch etc to remove this ice.

    Is there any other simple method & other means of removing this ice.

    Whay this ice gets formed & how to reduce that is other issue. But we can not control these activities & have seen that many a times the evap coil is even unaccessible due to very very odd loading in the cold stores inspite of racking systems & defined methodology of stacking in the cold stores.



  2. #2
    Join Date
    Mar 2006
    Location
    Norfolk
    Posts
    160
    Rep Power
    19

    Re: ice removal from evaporator coils

    Hi from best practices manual:-

    Types of Defrost

    There are four common methods of frost removal and a fifth
    hybrid method.

    Hot-Gas Defrost
    In a hot-gas defrost system, high-pressure, high-temperature,
    refrigerant vapor is discharged from the compressor and routed
    to and passed through the evaporator coil. The gas is often
    managed by a pressure regulator at the coil outlet, maintaining a
    pressure of 65 to 95 psig within the coil. In addition, there may
    be a master pressure regulator on the main hot-gas line that
    reduces pressure to about 100 psig. Any liquid or vapor
    refrigerant leaving the coil is typically returned in the coil
    suction line.

    Water Defrost
    In a water defrost system, warm water (typically 40 to 80°F) is sprayed over the coil surface.
    Although well or city water is sometimes used directly, there is usually a tank or pit where defrost
    water is stored. In a few cases, the water is heated by steam or electric resistance, but normally, it is
    heated using heat recovered from the refrigeration system. In most cases, a remote condenser sump
    serves double-duty as a defrost water tank, and water is heated
    during condenser operation.

    Air Defrost
    Air defrost is used in spaces where the refrigerant is below
    freezing and the air temperature is above freezing. The flow of
    liquid refrigerant is interrupted, and the fans continue to operate,
    blowing air over the coil surface to melt the ice.

    Electric Defrost
    Electric-resistance defrost is fairly uncommon in industrial
    refrigeration systems. Resistance elements are located on the evaporator coil, in contact with the
    metal. The elements heat the coil to melt accumulated ice. The size of the elements ranges typically
    from 10 to 40 kW per coil.

    Hybrid Defrost
    Although uncommon, some systems use a simultaneous combination of hot-gas and water defrost.
    A typical application would be a freeze tunnel where completely eliminating all frost quickly is
    critical to productivity.

  3. #3
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: ice removal from evaporator coils

    Quote Originally Posted by smpsmp45 View Post
    Is there any other simple method & other means of removing this ice.

    Whay this ice gets formed & how to reduce that is other issue.
    .

    If your system is not defrosting correctly, automaticaly then the defrost system needs looking at and repairing, adjusting or replacing to ensure it does work.
    If the system does defrost automaticaly but ice builds up in one area for no real reason then you need to look at what is causeing the ice.
    If the evap is near a door that allows air to enter the room and go to the evap then this in my opinion would be the major cause.

    Cheers taz.

  4. #4
    Join Date
    Sep 2006
    Location
    Venezuela
    Posts
    259
    Rep Power
    18

    Re: ice removal from evaporator coils

    Normaly one disign to have 4 defrost cycle every 24 hour.
    If the evaporator is getting to much ice it is due to the fact a lot of moisture is getting in the freezer

    Then you should increase the defrost cycle from 4 to 5 or to 6 . Of course you have to recheck the refrigeration load due to fact you are lowering the run time

    Normaly you install a vestibulo (room) in each door at 5°C to reduce the humidity getting in the freezer

  5. #5
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: ice removal from evaporator coils

    Quote Originally Posted by gwapa View Post
    Then you should increase the defrost cycle from 4 to 5 or to 6 . Of course you have to recheck the refrigeration load due to fact you are lowering the run time
    Or defrost longer on each cycle. You need to check the evap after a cycle to see if it is completely defrosted. To get the coil clean, you may have to run it through a couple of longer closed spaced defrost cycles. After this monitor the defrost for a week or so and adjust your times/cycles accordingly.

    Also, make sure all of the defrost controls are working as designed.

    Ken

  6. #6
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: ice removal from evaporator coils

    We do have defrost system which is efficient. But many a times due to negligence of maintenance staff, this phenomenon takes place. Then we have to use some other means to remove the ice. If we try out some external heating methods, the wire gets hard due to cold temp inside the room. Blow torch is again a danger situation. People use screwdrivers & all that stuff to remove the ice & that can damage the fans etc.

  7. #7
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    562
    Rep Power
    24

    Re: ice removal from evaporator coils

    Hi smpsmp45
    A few questions.
    How often does the ice build up and where abouts on the evap?
    What type of defrost do you have?
    How often do you defrost and how long is the defrost time?
    What is the negligence of the maintenance staff you talk about?
    Are the doos sealing properly?
    Generally ice build up is due to a problem with the defrost system, moisture getting into the room or moisture from the product.
    If you provide more info I am sure someone will solve your problem.
    Paul

  8. #8
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: ice removal from evaporator coils

    Quote Originally Posted by smpsmp45 View Post
    We do have defrost system which is efficient.
    If you are requiring manual chipping and a blow torch, your defrost system is not operating properly.

    What is your room temperature and the coil temperature? Also, what is the temperature and humidity of the space that opens to the freezer?

    You have one of two issues here. There is too much moisture getting into the room due to doors not properly sealed, infiltration from poorly sealed seams or doors being left open too long.

    Your coil is not being completely defrosted when you terminate defrost and go back into operation.

    What type defrost are we dealing with here? Air, hot gas, electric or water wash?

    If it is hot gas, is the hot gas pressure set correctly and is the coil getting hot enough to fully defrost the coil? Next is the valve sequence proper for the coil to sequence and isolate and clear the coil? What controls your defrost termination?

    If you are on electric defrost, are all of the heaters working? Is the defrost cycle long enough to clear the coil?

    There is no hard and fast rule for defrosting times or cycles. Typically you will start with 4, but some times you will have more or even fewer.

    If it is air defrost, what is the box temperature and how long do you cycle the liquid feed off?

    Using a heat source is a bad idea as it creates a thermal shock on the coil and can cause serious damage or failure. Also, using picks and chipping at the ice is dangerous as you could damage the finned surface or even penetrate a tube.

    In either case, these are not acceptable methods for a normal defrost.

    Ken

  9. #9
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: ice removal from evaporator coils

    Quote Originally Posted by smpsmp45 View Post
    We do have defrost system which is efficient. But many a times due to negligence of maintenance staff, this phenomenon takes place. .

    How many evaps are in the room?
    If there are more than one do they defrost at the same time?
    Make sure that all evaps defrost at the same time and see if the problems persist.
    Somtimes when evaps defrost at seperate times, the moist air from the defrosting evap can go straight to the running evap and cause ise to build up on it.

    taz.

  10. #10
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: ice removal from evaporator coils

    smpsmp45, in order to get some help, you need to answer a few questions which have been ask in the above post. We can't help anymore at this time until you provide the responses.

    Ken

  11. #11
    Join Date
    Apr 2007
    Location
    SOUTHAFRICA
    Age
    43
    Posts
    26
    Rep Power
    0

    Re: ice removal from evaporator coils

    may be the evap is under sized according to load

  12. #12
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: ice removal from evaporator coils

    Well Well. The defrost cycle works good in normal conditions. It is hot gas defrost system. & we do not face problems when it is operational. The issues come in when
    1. When the product is loaded at temperatures of more than -20 deg c. That also carries lot of water as we can see the cartons are wet. It is a typical mcdonalds distribution center.
    2. The loading in the cold store is generally at specified temperatures & the problem is not seen then.
    3. many a times Mcdonalds import some items which come in container loads. Then loading into the cold stores takes time due to earlier product inside. So they keep in the ante room till they rearrange the cold store products.
    4. The negligence now comes into play. The team on site is not checking at this time wherein max moisture goes in the cold store along with the wet cartons. They should manulaly defrost the system when this happens. But like all the mainteneance team, they wait till the problem becomes exceptionally bad.
    5. The only alternative left is to clean up the coil then.

  13. #13
    Join Date
    Mar 2004
    Location
    UK
    Posts
    624
    Rep Power
    21

    Re: ice removal from evaporator coils

    Hi

    Its seems to me that the coldroom is being missused,I had a situation where a freezer coldroom was to small for the stock at certain times of the day.The store would over stock the freezer cold room then store the excess in an ht coldroom until the shop floor freezers had been stocked.The moisture from the continuall door opening and wet boxes from Ht coldroom went straight for the coil.

    They kept calling me out until I said no more,I told them they needed a refrigerated trailer to empty and defrost coldroom.After four times in 6 months they soon got fed up and have now changed they delivery times and guess what,no more call outs.

    So I would spend some time in there taking pictures to prove its missuse.If you show them where there going wrong and give them a solution it may solve your problem.

    Regards Bernards

  14. #14
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: ice removal from evaporator coils

    Dear Bernards,

    Many thanks for the practical view. We shall do that

  15. #15
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: ice removal from evaporator coils

    Now we are beginning to see the issues. As noted above, the room was not designed for the way it is being used so you need to address how to use the room or how to adjust your procedures to make the room work.

    One easy solution may be to make it part of the standard procedures to have the "Operators" take the coils through a couple of manual defrost cycles to help clear the frost before it becomes a problem.

    Ken

  16. #16
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: ice removal from evaporator coils

    Infact we issue a standard procedure for daily/ six monthly checks etc. But that is kept in the files.

    Anyway issue still remains as to how to clean up the coil eventually.

  17. #17
    Join Date
    Mar 2004
    Location
    UK
    Posts
    624
    Rep Power
    21

    Re: ice removal from evaporator coils

    Hi

    If you must defrost the coil then I would valve the liquid line off and set defrost for 30min every hour for as long as the other evaps can hold the temp.Return with back mounted hot water sprayer and remove whats left if any.

    Lets face it,defrosting a freezer coldroom blower is one of the down sides of our job.

    Regards bernard

  18. #18
    Join Date
    Jan 2007
    Location
    Canada
    Age
    65
    Posts
    158
    Rep Power
    18

    Re: ice removal from evaporator coils

    You should change length of defrosting or/and frequency of defrosting. Coil should be defrosted before it is frost plugged(no space between fins). Additional frost on the coil require additional time to melt it.

  19. #19
    stepperider's Avatar
    stepperider Guest

    Re: ice removal from evaporator coils

    Gentlemen

    I am from the tropics and was just posted to work in a brewery cold-cold Mongolia. We have an NH3 system with evaporative condenser using fan (winter mode) and fan+water (summer mode). Cutoff for winter/summer is -9.9 deg C (14.2 deg F). The water is pump from an indoor sump to the evaporative condensor outside.

    However, I find that the evaporative condenser may be undersized (high discharge pressure +18-19 bars!), and sometimes turn on the water pumps while the outside air temperature is -15 to -18 deg C (5 to 0 deg F).

    What I would like to learn from your experience is: at what lowest outside air temperature do you continue to spray water without fear of the condensor coils developing ice?

    We do not have any defrosting device installed or heater in the water basin. Could anyone point me to the right direction on this.

    Thanks a million.

  20. #20
    Join Date
    Jan 2007
    Location
    Canada
    Age
    65
    Posts
    158
    Rep Power
    18

    Re: ice removal from evaporator coils

    Quote Originally Posted by stepperider View Post
    Gentlemen

    I am from the tropics and was just posted to work in a brewery cold-cold Mongolia. We have an NH3 system with evaporative condenser using fan (winter mode) and fan+water (summer mode). Cutoff for winter/summer is -9.9 deg C (14.2 deg F). The water is pump from an indoor sump to the evaporative condensor outside.

    However, I find that the evaporative condenser may be undersized (high discharge pressure +18-19 bars!), and sometimes turn on the water pumps while the outside air temperature is -15 to -18 deg C (5 to 0 deg F).

    What I would like to learn from your experience is: at what lowest outside air temperature do you continue to spray water without fear of the condensor coils developing ice?

    We do not have any defrosting device installed or heater in the water basin. Could anyone point me to the right direction on this.

    Thanks a million.
    Condenser coils will never develop ice, because their temperature are above 0 deg C. Condenser water has positive temperature as well. Make sure that pump will cut off first, otherwise you have opportunity to freeze fan blades.

  21. #21
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: ice removal from evaporator coils

    Hello Sanjay,

    I had gone through your thread. First thing is that I fully agree with Ken. You have set the timing of the defrost cycle after assessing the ice formation. Forming of ice to such an extent so as to defrost with blow torch is not correct. In addition to other problems, it will damage the coil fins.

    While designing the cold room, you must have been provided with some requirement details. If loading in wet boxes were not there, you should make it very clear to your customer that what he is doing is wrong and harmful to the plant and that you can not be held responsible for such things.

    I would advice you to reassess the time period of defrost and and also the time required for running the defrost. I hope the it is electrical defrost that you have.

  22. #22
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Thumbs up Re: ice removal from evaporator coils

    smpssmps45
    I note that you started your thread in the middle of september.
    From all the advise you have had have you been able to resolve anything?
    It is a real pain when evaps freeze up isn't it. You can be the most diligent Engineer and still get caught out sometimes, so don't be to hard on your maintenance staff. Unless of course you suspect that they really are the problem?
    I myself have been in cooler pods Kangoing the sheet ice off of the pod floor. BUT.. As has been said! If it is the evap coils that are blocked. That's a different story!
    You don't say how your coldstore chamber is designed, with regard to how the evaps are mounted.
    Are they suspended (eisier to deal with), or pod mounted with access from the side of the pod. Via a INSULATED DOOR ( that can be relevant).
    Anyway a practical solution is to isolate the evap from it's cold enviroment. Not so easy sometimes, so if it is the pod type. Get some large suitable sheets of polystrene or similar.
    Place these across the face of the pod and retain in place. Only you can decide as to how.
    On the suspended type ( these are much more common. Particularly on smaller applications) Borrow from despatch a roll of shrink wrap. Wrap up the whole evaporator in the cling film.
    Once either method has achieved thermal isolation.
    Initiate manual defrost and cook ( sit down, put the kettle on and wait.)
    Basically only you will be able to tell when "cooking is complete" by visually checking the coil status.
    The beauty of this method is you can apply the heat locally without to much heat introduction to the rest of the chamber.
    Hope this is of help?
    Grizzly

  23. #23
    Join Date
    May 2007
    Location
    Pennsylvania
    Age
    51
    Posts
    113
    Rep Power
    17

    Re: ice removal from evaporator coils

    Quote Originally Posted by Sergei View Post
    Condenser coils will never develop ice, because their temperature are above 0 deg C. Condenser water has positive temperature as well. Make sure that pump will cut off first, otherwise you have opportunity to freeze fan blades.
    True Sergei, but if you have a condenser that is last on the lead list it is certainly possible to freeze the sump. I know, because we made a nice ice cube out of the sump of one condenser last year when the temperature dipped below 0f for a few days. There was a pool of liquid water extending about 12" around the sump heater but the rest of the pan was frozen. Looking back through the logs we found that the pump had not been called for in over 48hrs.

    Now we drain 1-2 of our 3 condensers for the winter.

    Winter is also a good way to find minor water leaks on condensers - I have seen some really nice ice flows build up from a drip a minute leak!

  24. #24
    Join Date
    Jan 2007
    Location
    Canada
    Age
    65
    Posts
    158
    Rep Power
    18

    Re: ice removal from evaporator coils

    Quote Originally Posted by brian_chapin View Post
    True Sergei, but if you have a condenser that is last on the lead list it is certainly possible to freeze the sump. I know, because we made a nice ice cube out of the sump of one condenser last year when the temperature dipped below 0f for a few days. There was a pool of liquid water extending about 12" around the sump heater but the rest of the pan was frozen. Looking back through the logs we found that the pump had not been called for in over 48hrs.

    Now we drain 1-2 of our 3 condensers for the winter.

    Winter is also a good way to find minor water leaks on condensers - I have seen some really nice ice flows build up from a drip a minute leak!
    Hi, Brian.
    Water sumps of your refrigeration plant are outside, but stepperider's water sump is inside. This is a huge difference. I'm surprised that somebody designed the plant in Pennsylvania and located condenser sumps outside.

  25. #25
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: ice removal from evaporator coils

    Sergei.
    In U.K. All our evaporative towers are outside, or at least I have never seen one inside yet!
    I have not seen anything as harsh as Brian describes, although some of my colleages in the colder regions of our isles may disagree!
    I have seen ice damaged sumps due to faulty frost stats though.
    Brian you refer to leak identification due to ice forming.
    Try 2 young "Chlorination Experts" trampling through the sump in their "Hob Nail Boots". Quote "it wasn't Me"
    Grizzly

  26. #26
    Join Date
    Jan 2007
    Location
    Canada
    Age
    65
    Posts
    158
    Rep Power
    18

    Re: ice removal from evaporator coils

    Quote Originally Posted by Grizzly View Post
    Sergei.
    In U.K. All our evaporative towers are outside, or at least I have never seen one inside yet!
    I have not seen anything as harsh as Brian describes, although some of my colleages in the colder regions of our isles may disagree!
    I have seen ice damaged sumps due to faulty frost stats though.
    Brian you refer to leak identification due to ice forming.
    Try 2 young "Chlorination Experts" trampling through the sump in their "Hob Nail Boots". Quote "it wasn't Me"
    Grizzly
    Grizzly.
    I'm talking about water sump, but not about evaporative tower. Condenser itself, certainly, should be outside. Water sump can be located at the bottom of condenser(outside) for warm climate and inside the warm building for cold climate.

  27. #27
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: ice removal from evaporator coils

    Sergei
    Sorry crossed wires. I have never seen one with a remote sump. Have I got that correct?
    The design is different to anything I have seen.
    Have you or anyone reading this a photo?
    Iv'e led a sheltered life you see! Pun Intended!
    Respect- Grizzly.

  28. #28
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: ice removal from evaporator coils

    We are getting off-topic a bit guys. Ice removal from evaporator coils is different than indoor remote water sumps.

    Grizzly, a remote sump (or indoor sump) is simply a water tank and pumps for the evaporative condenser water supply (located in a warm environment like the engine room). This is very common in colder climates where the system operates year round.
    If all else fails, ask for help.


  29. #29
    Join Date
    Dec 2007
    Location
    malaysia
    Posts
    159
    Rep Power
    17

    Re: ice removal from evaporator coils

    smpsmp45,

    1] curious to me that you depend on maintenance person to handle defrost. aren't that to be automatically done?
    2] storage management is poor; has to improve the method.
    3] have u considered lowering ante room temp?
    4] can u check on SST of system?
    5] can u check incoming product temp against design assumptions?

    above will define your focus point in troubleshooting.

  30. #30
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: ice removal from evaporator coils

    We use a steam heater like this one
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  31. #31
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: ice removal from evaporator coils

    As I had noted in an earlier post, defrosting with a steam system is not a good approach. If you hit the coil too fast or too hard with the steam, you can thermally shock the oil which can lead to premature metal failure.

    Your best bet is to either get the defrost working properly or get the humidity source under control.

    ken

  32. #32
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: ice removal from evaporator coils

    Ken with all my respect but I don't think we can heat that much the oil that it reaches a higher temeprature then discharge temperatures.
    Because that's the temperature for what's it designed for
    Further, we use it to melt the ice, not to heat up the copper or the steel of the evaporator.
    We direct it to the ice of course and you heat of course the fins but you always can touch the fins with your bare hands. It doesn't become that hot.
    Also, the heat is spread very equal over the fins and it distributes the heat equally.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  33. #33
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: ice removal from evaporator coils

    Peter if you have an untrained operator (and we all know that there is no such thing), they can put so much steam on the coil that it can thermally shock it, especially if it is not heated evenly. Too much heat in one area can create thermal stress which can lead to a material failure.

    So yes, in the hands of a properly trained person, a steam generator can be used. But look at the steam again....more humidity in the space where you do not need it, for the other coils or the only coil to deal with. I still say that the correct procedure is to locate the design or operating problem.

    I have in a rare situation, used steam to get rid of ice, but I still located the problem rather than continue to use steam for a crutch.

    Ken

  34. #34
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: ice removal from evaporator coils

    Ken, I agree with you for 100%, the cause of the problem must be solved.
    And certainly, steam as a standard is not done.
    We only use this small device from Karcher to defrost after a resistance failure or something similar when the coil has blocked up with ice.
    If you use water in a freezer, then the whole floor becomes an ice-skating rink.
    In a small counter, sometimes the sewage are too small to use water.
    We use it also to disinfect the small drain pans in counters.
    You sometimes find strange creatures in the drain pans.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  35. #35
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: ice removal from evaporator coils

    In a case like these ones
    Attached Images Attached Images
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  36. #36
    Join Date
    Dec 2007
    Location
    Volos, Greece
    Posts
    46
    Rep Power
    0

    Re: ice removal from evaporator coils

    Quote Originally Posted by Peter_1 View Post
    In a case like these ones
    Oh ! This needs a new cold room !!!! Defrost all !

Similar Threads

  1. Replies: 12
    Last Post: 15-09-2007, 01:30 AM
  2. Oil removal from Ammonia plant
    By psrao in forum NH3
    Replies: 6
    Last Post: 23-03-2007, 09:59 PM
  3. 5h Main Bearing Removal And Inserts
    By altaf22m in forum Commercial
    Replies: 5
    Last Post: 07-03-2006, 04:54 AM
  4. 5h Main Bearing Removal And Inserts
    By altaf22m in forum Industrial
    Replies: 1
    Last Post: 06-03-2006, 09:15 PM
  5. Removal of migrated oil in dimple plate milk vat
    By Cary in forum Trouble Shooting
    Replies: 10
    Last Post: 15-05-2004, 05:36 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •