    High humidity in cold room



    Hi Everyone,

    I have been requested by a client to check a cold room with a high humidity problem. The water condenses on the ceiling and walls. When the air curtain installed on the warmer side of the door is switched on while the door is open, the condensation is worse.

    Any ideas what causes the above.

    Regards

    nimamu



  2. #2
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: High humidity in cold room

    What are the required RH and the temperature of the Cold Room. Further how is the high humidity being achieved. Once these are known, some solutin can be advised.

  3. #3
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: High humidity in cold room

    Hi there,

    This is because the moisture content of the area you are located is very high. When the air curtain starts, outside air goes into the cold room. This high moisture condenses on cold surfaces.

    Cheers
    Even Einstein Asked Questions

  4. #4
    Join Date
    Mar 2006
    Location
    dallas, texas
    Age
    75
    Posts
    108
    Rep Power
    19

    Re: High humidity in cold room

    I have always found that air curtains are of little help in moisture control between a warm area and a cold area, that is open much of the time.

    The room air acts like a cold front moving into an area that is warm. the cold area moves outward near the ground or in this case near the floor and the warm air with high humidity comes over the top to replace the volume of cold drier air leaving the cooler. Remember everything in nature seeks to be in balance. espically the vapor pressure..

    We have used an ante room design between the two areas always open and then put a cooling evaporator blowing towards the warm side opening or door.
    This allows the incoming air replacing the escaping cold air to be partially dehumidified before entering..

    In addition, if you use cooling evaporators blowing near the ceiling they tend to wipe the high humidity from the cold surfaces, alleviating some of this moisture problem

    Try to understand the vapor pressure issue between the two areas and yo will then solve your moisture delimma.

    Hope this helps
    Bruce.

  5. #5
    Join Date
    Apr 2006
    Location
    Unite Arab Emirates
    Posts
    6
    Rep Power
    0

    Re: High humidity in cold room

    Hi Bruce,

    Many thanks for the analysis. Will keep all advised with update once the issue is solved.

    Regards

    nimamu

  6. #6
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    562
    Rep Power
    24

    Re: High humidity in cold room

    Hi
    Does the room have condensation in there all the time or does it only appear when the door is open.
    Air curtains are a waste of time and I have found that clear plastic strips work better if the door is left open a lot.
    Another cause could be the product in the room.
    What is stored in the room and what is the desired room temp.
    If the evap is close to the roof of the coolroom and you are running a very cold evap temp the roof of the room will get very cold and if the product is hot and gives off a lot of moistue condensation will occur.

  7. #7
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: High humidity in cold room

    Hi Nimamu, I tnd agree with Paulz that air curtain is waste of time, add slatted curtain instead. Secondly, sounds like sensible cooling ratio is too high, either add more compressor HP to decrease suction, or slow evap fans with filters or speed control. Basically you have to condense moisture on coil fins to remove it from room.
    regards Magoo

  8. #8
    Join Date
    May 2007
    Location
    Lincoln, England
    Age
    66
    Posts
    31
    Rep Power
    0

    Re: High humidity in cold room

    Hi Nimamu

    A conventional air curtain is a waste of time as this can often introduce more moisture into the cold room - despite manufacturers claims.

    The modern method of reducing ingress of moisture into cold stores is to use very dry air from a desiccant dehumidifier. A number of leading UK supermarket chains are now using this method in their cold storage depots The dry air duct outlet is designed to produce a curtain of dry air down across the face of the doors (on the warm side). I have recently supplied a number of desiccant dehumidifiers for use in supermarket cold stores where the DH units supply air at minus 25°Cdp. This system dramatically reduces ice build up on door frames, ceilings and floors (health & safety) and also improves efficiency of dx cooling coils (reduced latent load and defrost cycles). If the dehumidifiers are located in the loading area (2-5°C) then these areas also benefit from a much reduced humidity.
    Last edited by Psychro; 17-09-2007 at 01:00 AM. Reason: add info

  9. #9
    Join Date
    Apr 2006
    Location
    Unite Arab Emirates
    Posts
    6
    Rep Power
    0

    Re: High humidity in cold room

    Hi Psychro,

    Your idea to use dry air is excellent. Thanks a lot for that idea. Will recommend this to the client.

    Regards

    Nimamu

  10. #10
    Join Date
    May 2007
    Location
    Lincoln, England
    Age
    66
    Posts
    31
    Rep Power
    0

    Re: High humidity in cold room

    Hi Nimamu

    Please let us know how you get on !

  11. #11
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: High humidity in cold room

    Dear Psychro,
    Can you throw more light on this & what is that system The air needs to made dry? You need separate compressors for air? We too are desperately loking for a sustainable solution. We tried rapid doors, & the problems got reduced drastically. but your suggestion seems more efective.

  12. #12
    Join Date
    May 2007
    Location
    Lincoln, England
    Age
    66
    Posts
    31
    Rep Power
    0

    Question Re: High humidity in cold room

    Hi smpsmp45

    When cold store doors are opened, a turbulent exchange of air occurs across the door space. Moisture from outside air condenses on the cold store floor and other surfaces producing ice, frost and even snow. Moisture entering a cold room will also freeze on evaporator coils. Frosted coils are inefficient and defrosting is expensive.

    A desiccant dehumidifier operates by extracting moisture in its vapour state so is able to effectively remove moisture without producing condensation (or frost). It is capable of supplying air at a very low dewpoint (< -35°Cdp). Provided the dehumidifier process air inlet is already at a reasonable humidity ratio (7 to 10°Cdp), a dry air outlet at -20°Cdp is easily attainable. In industrial drying systems this is normally achieved by using a pre-cooling coil.

    In large cold storage depots, there is often a loading area which separates the cold store from ambient. The loading area is normally cooled to 2 to 5°C. If a desiccant dehumidifier is installed in the loading area and takes its suction from this space, the dry air outlet will be around -25°Cdp. This air is then ducted to above the cold store doors (loading bay side) to produce a curtain of very dry air. The unwanted moisture vapour from the dehumidifier is ducted to ambient.

    The dehumidifier is effectively dehumidifying the loading bay area whilst also supplying the driest air to where it is needed (above the cold store doors). The system is better used in conjunction with fast closing doors and whilst it greatly reduces ice build up, the biggest advantage is energy savings by allowing evaporator coils to do what they were designed to do - sensible cooling.

    If you want to know more about desiccant dehumidifiers there is a fair bit available on the web (Google search) but please spell desiccant correctly – one S, two C’s !!!!

    Regards
    Psychro

  13. #13
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: High humidity in cold room

    Many thanks Psychro

  14. #14
    Join Date
    Dec 2007
    Location
    Volos, Greece
    Posts
    46
    Rep Power
    0

    Re: High humidity in cold room

    A desiccant dehumidifier is the best solution but you can try also to set the evaporatior fans in continious mode (only stop at defrost) this will help a little.

  15. #15
    Join Date
    Dec 2007
    Location
    malaysia
    Posts
    159
    Rep Power
    17

    Re: High humidity in cold room

    but, strange in Asia, eventhough is highly humid, situations are rather different.

    could you advise?

    i've not receive info on installation of desiccant drier.

  16. #16
    Join Date
    Mar 2004
    Location
    UK
    Posts
    624
    Rep Power
    21

    Re: High humidity in cold room

    Hi
    It could also be the defrost termination set to high,with the fans switching on to early blown warn air around cold room.Also when was the last time the coldroom was closed down, defrosted and dried.

    Regards Bernard

  17. #17
    Join Date
    Oct 2007
    Location
    Newastle Upon tyne
    Posts
    4
    Rep Power
    0

    Re: High humidity in cold room

    Sounds like the ingress of warm moist air into the room when the doors are opened... strip curtains help but if the door is left open for too long, the inevitable will happen.
    fitting a "bubble" or additonal entry that is dehumidified will help this, although it can be costly and should really have been thought about during the desgn stages.
    somebody posted earlier that hot products will cause high moisture also... very true, should your client be blast chilling their product before it goes into cold storage?

  18. #18
    Join Date
    Jan 2007
    Location
    india
    Posts
    9
    Rep Power
    0

    Re: High humidity in cold room

    Hi
    pl can any one will paste here

    wet bulb , dry bulb chart to calculate the humidity
    i will appricate it
    sidhartha

  19. #19
    Join Date
    Oct 2004
    Location
    USA
    Age
    65
    Posts
    24
    Rep Power
    0

    Re: High humidity in cold room

    Hello all,
    Better late then never?
    I deal in alot of 4C cold rooms.
    We have something we call "cold fingers".
    It is bare copper coil without fins added just upstream
    of the evap coil. We get water in the air to condense without as much heat transfer. Refrigerant to the DH coil and the EVAP coil is controlled independently. There you have it........my 2 cents.

  20. #20
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

  21. #21
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: High humidity in cold room

    Quote Originally Posted by nimamu View Post
    Hi Everyone,

    I have been requested by a client to check a cold room with a high humidity problem. The water condenses on the ceiling and walls. When the air curtain installed on the warmer side of the door is switched on while the door is open, the condensation is worse.

    Any ideas what causes the above.

    Regards

    nimamu
    What are the temperatures of the air entering/leaving the coil?

    What humidity level are you trying to achieve?

Similar Threads

  1. Cold Room Design - minus 25deg C
    By vijay_study in forum Fundamentals
    Replies: 34
    Last Post: 11-11-2009, 07:12 AM
  2. Cold room dimensioning - ratio volume air flow
    By MrReds in forum Technical Discussions
    Replies: 11
    Last Post: 17-11-2007, 10:51 PM
  3. Cold Room Design
    By vijay_study in forum Fundamentals
    Replies: 11
    Last Post: 09-07-2007, 08:11 AM
  4. LG Capacitor - Room not cold
    By kelamel in forum Trouble Shooting
    Replies: 8
    Last Post: 21-10-2006, 10:50 AM
  5. Installation of cold room
    By Josip in forum Legal-Business-Marketing
    Replies: 12
    Last Post: 12-03-2006, 09:20 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •