    Cycling Compressor



    I have a compressor cycling on the high pressure switch and the compressor is extremely hot. There is no colling. Any suggestions?



  2. #2
    Join Date
    Jul 2006
    Location
    USA
    Age
    73
    Posts
    865
    Rep Power
    26

    Re: Cycling Compressor

    Quote Originally Posted by Doylee View Post
    I have a compressor cycling on the high pressure switch and the compressor is extremely hot. There is no colling. Any suggestions?
    It would sound like you have a Condenser that that is not working.
    However you MUST provide more details about the system in order for us to help you.

  3. #3
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Cycling Compressor

    The compressor should not cycle on the HP switch as this is a safety.

    High discharge pressure is caused by a condenser problem of a discharge blockage.

    What type condenser do you have?

    Ken

  4. #4
    Join Date
    Jan 2007
    Location
    Chesterfield, UK
    Posts
    79
    Rep Power
    18

    Re: Cycling Compressor

    Or there could be too much refrigerant in the system.
    Or the condenser unit could be undersized.
    or it could be shut up in a little room(just had this one myself tee hee)
    or wrong refrigerant in the system.
    or HP switch faulty.

  5. #5
    Join Date
    Apr 2007
    Location
    SOUTHAFRICA
    Age
    43
    Posts
    26
    Rep Power
    0

    Re: Cycling Compressor

    firstly it should not cycle on hp due to it not being a part of controls but a safety precusion,

  6. #6
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Cycling Compressor

    Most common cause if faulty condenser fan or blocked condenser coil (fins blocked with dust and dirt)
    See if the condenser is clean and the fan is working.
    edit: But I have to add, if you didn't check these things, how would you know it's cycling on HP, could be cycling on LP?

  7. #7
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: Cycling Compressor

    As said before, this is a safety issue and so the HP switch should be a MANUAL reset, not an AUTO reset.....these are for cycling fans for head pressure control.

  8. #8
    Join Date
    Aug 2007
    Location
    Malawi
    Age
    41
    Posts
    19
    Rep Power
    0

    Re: Cycling Compressor

    if you say the compressor is too hot, it could be cycling on the thermal overload,i suggest you let the compressor cool, than you can start trouble shooting .some of the possible causes the have been listed by other posts.
    however a leak in the suction can make the compressor to suck in non condensibles , creating high pressure and making the compressr hot.Z(checking will do you no harm)

Similar Threads

  1. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  2. Mitsubishi compressor lock
    By marc5180 in forum Air Conditioning
    Replies: 29
    Last Post: 08-10-2007, 05:48 PM
  3. Compressor Cycling
    By nlester in forum Commercial
    Replies: 2
    Last Post: 22-05-2007, 04:20 PM
  4. Compressor short cycling....
    By sbessettejr in forum Trouble Shooting
    Replies: 10
    Last Post: 02-04-2007, 05:09 PM
  5. Compressor pumping efficiency
    By shogun7 in forum Fundamentals
    Replies: 0
    Last Post: 25-02-2004, 10:50 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •