    broken valves, but why?



    Got called to a fabdec dx milktank and icebuilder on friday an this is what i found. system has been in for twelve years. the compressor next to it doesn't pump too good either, would not pull a vacuum. prestcold/copeland pl20x 0027. on R22.
    See next post also

    Cheers Jon
    Attached Images Attached Images
    Last edited by monkey spanners; 26-09-2007 at 11:10 AM.



  2. #2
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: broken valves, but why?

    Quote Originally Posted by monkey spanners View Post
    Got called to a fabdec dx milktank and icebuilder on friday an this is what i found. system has been in for twelve years. the compressor next to it doesn't pump too good either, would not pull a vacuum. prestcold/copeland pl20x 0027. on R22.
    See next post also

    Cheers Jon

    Looking at the photos I think they have done well.
    If you look at the reeds you will see that they have simply worn away from use.
    The seat has slowly worn a groove that has finaly given up.

    They look clean but the one on the right seems to have failed towards the end.
    Just old age.
    I bet a new valve plate fitted will have it back like new.

    Cheers taz.

    Thats proper fridge work that is.
    You can't repair a hermetic like that.
    Last edited by taz24; 09-09-2007 at 06:27 PM.

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: broken valves, but why?

    This is the pipe work where the icebuild 't's into the suction line. the system with the duff compressor only had 1.5kg R22 in it, 5 or 6Kg would be more likely. i think the oil has been running into the icebuilder suction when the system is running the tank and on starting the icebuilder has been slugging the compressor. With the low charge i suspect more oil could have run down the icebuilder suction (which slopes th wrong way. the pipework goes out the back wall which the picture doesn't show too well. Its 1 1/8"
    Your opinions please

    Cheers Jon
    Attached Images Attached Images

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: broken valves, but why?

    Cheers Taz, it doesn't show in the picture but the suction valves have been bent into a dome shape over the port. I think its been pumping liquid, and most likely oil, unless the customer hs been running the tank empty, will ask on monday when the new compressor goes on. Its struggling to cope on one so its a quickest rather than cheapest fix this time. just don't want the new one going the same way

    Cheers Jon

  5. #5
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: broken valves, but why?

    Quote Originally Posted by monkey spanners View Post

    and most likely oil, unless the customer hs been running the tank empty, will ask on monday when the new compressor goes on.

    Cheers Jon

    From your other post with, with the pipe run and the oil I would tend to agree with you and if the valve is domed then that would confirm it evan more.
    I would look then to why it only had a part charge in it. Was it leaking or has it been charged with more and more oil due to it collecting in the evap, untill finaly all the oil returned back to the comp.

    As for the farmer running the tank dry, does it have an ice bank stat fitted and if yes does it work?

    taz

  6. #6
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: broken valves, but why?

    Its a direct expansion tank (Dx) no water, just a curved stainless plate forming the botttom of the tank, the milk is in direct contact with this, no milk no load. Needs 5/10% filing before turning on. The rotalock valve on the reciever looks like the leak point will be able to check when pressure tested tomorrow.

    Jon

  7. #7
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: broken valves, but why?

    Quote Originally Posted by monkey spanners View Post
    Its a direct expansion tank (Dx) no water, just a curved stainless plate forming the botttom of the tank,
    Jon
    Ah ok then.
    Cheers taz.

  8. #8
    Join Date
    Aug 2007
    Location
    Malawi
    Age
    41
    Posts
    19
    Rep Power
    0

    Re: broken valves, but why?

    from your other post i think the compressor was pumping liquid refrigerant that is why it broke the valves

Similar Threads

  1. Stainless steel valves
    By Tycho in forum NH3
    Replies: 5
    Last Post: 05-11-2008, 02:16 PM
  2. Hinari and how far to open valves
    By stryker in forum Air Conditioning
    Replies: 6
    Last Post: 14-04-2008, 01:47 AM
  3. dan foss tx valves
    By fuzzy in forum Trouble Shooting
    Replies: 7
    Last Post: 02-10-2007, 01:11 PM
  4. Suction Stop Valves
    By frank in forum Air Conditioning
    Replies: 10
    Last Post: 02-08-2006, 11:04 PM
  5. Glycol water valves
    By eng_ab in forum Industrial
    Replies: 2
    Last Post: 03-06-2005, 09:15 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •