    Snow Problems



    relatively new installation research building that uses chiller that supplys chilled water to coils at 50*f with face and bypass steam system for heat. The problem Im experiencing is the plenum chamber seems to be to short and on heavy snow days the plenum accumulates lots of snow that saturates the filters and slings freezing water and trips the freeze stat any suggestions on how could remedy.



  2. #2
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24
    Hi,dar
    I take it that the snow is comming in from outside? The chilled water is at too high a temp to freeze moisture from the air.
    Regards. Andy.

  3. #3
    dar's Avatar
    dar Guest

    snow problems

    Yes Andy the snow is coming from outside theres a short space between the outside wall and the plenum chamber. about 3feet. after which the filters are located which are currently paper type 24"times24"by2" after the filters there is a heating coil which uses steam at 13psi which is a face and bypass type system a problem i beleive is the configuration of the steam coil only directs heat downstream of the coil and none of the heat radiates back towards the plenum chamber and as a result im getting piles of snow at filter supply side which being paper buckle and allow freezing water to reach freezestat tripping out unit.

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51
    The steam coil after the filters will be either pre-heat or heat and will offer no protection to the filters at all. Protection for the filters (and for the steam coil if it is off) should be handled by a frost coil or heater tape prior to the filter and should be controlled by a freeze stat set at +5C or thereabouts.

    Without frost protection you are in danger of losing you steam coil if it is ever turned off.

    Frank

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    If I understand correctly, we are talking about the fresh air intake going into a mixing chamber. I would suggest a hood on the outside.

  6. #6
    Join Date
    Jun 2001
    Location
    Huntington Beach, CA, USA
    Age
    80
    Posts
    17
    Rep Power
    0
    Questions:

    1. What is the cfm entering the duct from outside?
    2. What size is the duct?
    Thanks, Tom
    Tom D.

  7. #7
    Join Date
    Jul 2002
    Location
    washington
    Age
    37
    Posts
    77
    Rep Power
    22
    Couldnt you use some sort of Anti-freeze in small amounts?
    one mans trash is another mans treasure

Similar Threads

  1. Replies: 10
    Last Post: 18-03-2006, 07:35 PM
  2. Problems LG don't want you to know about
    By Andy W in forum Air Conditioning
    Replies: 11
    Last Post: 16-02-2006, 04:52 PM
  3. Oil return problems
    By Peter_1 in forum Industrial
    Replies: 37
    Last Post: 23-08-2004, 11:30 PM
  4. Snow
    By Derek in forum Technical Discussions
    Replies: 2
    Last Post: 24-11-2002, 01:32 AM
  5. oil pressure problems on air dryer
    By edge in forum Trouble Shooting
    Replies: 1
    Last Post: 16-07-2002, 02:10 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •