    Sabroe HPC 106 on CO2



    First things first hi all,
    Now down to business, I've been looking after fridge systems for 25 years, at the moment I look after only one site, which is of a reasonable size consisting of 2 Stal mini screws S24 and a R5 MK2 for the vertical scrape coolers. 1 frigoscania plant with a Sab 163 hf and a CO2 plant with a SMC 116 e and 2 HPC 106s's both suppling cooling for 2 Samifi's plate freezers. A coldstore with 2 bitzer screw on NH3 and A/C for the production area being supplied by 2 Grasso recep's. I took part in the commisioning of the the CO2 plant while working for York and to be honest was never overly impressed with the plant. The oil recovery was always an arse on the CO2 side. I have since modified and has been proven to be ok for the last 8 months, plus other minor problems I've had to sort. The plant is now about 2 1/2 years old and since being employed by the site I've kept on top of all the servicing. First I carried out an inspections on all of the comps, a top end service and an oil change on the NH3 comp after finding 3 broken suction valves and numerous valve spring broken. After completing the oil change and top inspections on the CO2 comps everything looked in order. Well I thought, today after being able to shut the plant down I took the opportunity to carry out a oil filter change and top end service on the No1 CO2 comp. All was going well untill I took the last valve out to find mild pitting in the piston's crown, thinking a suction valve was broke but no, so I pulled the liner out to find the rings shattered, plus the ring grooves on the piston looked like they had melted in a fuuny way. Being curious I pulled out all the other liners to find every single piston ring had shattered. I mean each ring in about 6 or 7 pieces, no valves were broken not even a spring, all the liners are ok except for the melted one. York had previosly replaced a comp due to failure, not this one though. I was just wondering if there was anyone out there that has had much to do with HPC106's comps on CO2 and there experiences of them.

    Cheers for looking Dober49.



  2. #2
    Join Date
    Nov 2006
    Location
    Kettering
    Age
    56
    Posts
    5
    Rep Power
    0

    Re: Sabroe HPC 106 on CO2

    Hi all again
    Looking into it my basic conclusions are, that the discharge limits are set to high resulting in high discharge pressures. Due to the nature of the application, basicaly the site have been putting to much product loading on to the plant. At commisioning York run the plant at -10 condensing on the cascade cooler, I did lower this to -18, at the time to save on energy. After looking at things I see this should be the norm. At the moment discharge limiting is at 33 barg and the high alarm is at 35 barg. I think I'll be lowering this to 27 barg limiting and 30 barg on the high alarm to save the compressors from this happening again.
    Any additionaly info would be greatly recieved.
    Cheers Dober49

  3. #3
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Sabroe HPC 106 on CO2

    Quote Originally Posted by Dober49 View Post
    Hi all again
    Looking into it my basic conclusions are, that the discharge limits are set to high resulting in high discharge pressures. Due to the nature of the application, basicaly the site have been putting to much product loading on to the plant. At commisioning York run the plant at -10 condensing on the cascade cooler, I did lower this to -18, at the time to save on energy. After looking at things I see this should be the norm. At the moment discharge limiting is at 33 barg and the high alarm is at 35 barg. I think I'll be lowering this to 27 barg limiting and 30 barg on the high alarm to save the compressors from this happening again.
    Any additionaly info would be greatly recieved.
    Cheers Dober49

    Hi Dober

    It is the general accepted that Co2 recips need a 10000 hours overhaul each year, all but a shaft out, shell bearings and piston rings along with piston rings.

    If this is carried out each year the compressor will run well.

    The Co2 is a very dry refrigerant causing frictionwearing rings and linners quickly.

    Also the high pressure causes a lot of load on the bearings, so they need changed at a shorter interval.

    Hope this helps.

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  4. #4
    Join Date
    Nov 2006
    Location
    Kettering
    Age
    56
    Posts
    5
    Rep Power
    0

    Re: Sabroe HPC 106 on CO2

    Hi Andy
    Thanks for that, i'll be keeping a closer eye things from now on.
    The only thing that concerns me, is that it looks like the piston ring grooves worn down causing the rings to shatter.
    I can only think of high discharge pressures causing this or liquid but I know thats not the case, i've spoken to sabroe who will be coming back to me with the correct spec for this comp.
    As I said before I havn't got a great confidence in the york office I was dealing with.
    Heres a little pic.
    Note the groove wear.
    By the way want would you call excessive discharge pressure on CO2 plant ?
    Attached Images Attached Images
    Last edited by Dober49; 10-09-2007 at 01:39 PM.

Similar Threads

  1. Sabroe 202 LM
    By nh3wizard in forum Industrial Compressors
    Replies: 11
    Last Post: 10-03-2011, 05:35 PM
  2. Sabroe Recip
    By Andy in forum Industrial Compressors
    Replies: 36
    Last Post: 06-03-2008, 02:29 AM
  3. Sabroe flake ice machine
    By claude11 in forum Industrial
    Replies: 5
    Last Post: 21-12-2007, 08:10 PM
  4. Sabroe TSMC108S
    By guidel in forum Industrial Compressors
    Replies: 0
    Last Post: 13-06-2007, 10:38 AM
  5. Sabroe CMO28 mk2 comp unloaders
    By GENGUS in forum Technical Discussions
    Replies: 2
    Last Post: 17-11-2006, 01:18 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •