Thread: Star High Flux Chiller
07-09-2007, 06:49 PM #1
We have a problem with a Star manufactured High Flux Chiller.
The chiller operates on R22 and uses a Danfoss PHTQ expansion valve. The PHTQ is controlled by a Star PCB which has failed and the board is apparently no longer manufactured.
As far as I can tell the board takes a signal from a thermistor in the heat exchanger and the valve opening is controlled by this. I think the logic of the High Flux is that it is almost flooded and the heat exchanger is like an LPR vessel.
Can anyone expand on the operation of the PCB so we can come up with some sort of alternative. At the moment we are not really getting any info from the manufacturer.
07-09-2007, 09:16 PM #2
Re: Star High Flux Chiller
I think you want a danfoss EKC 315A for TQ valves
08-09-2007, 11:08 AM #3
Thanks for the feedback
I think the EKC is a superheat reference controller. What I have is a system were the valve opening is controlled based on the liquid level in the heat exchange vessel, the sensor is immersed in the refrigerant ( I think that there were not many of these chillers manufactured) this is the only control input.
I could maybe use this controller and modify elements of the plant to suit. I was mainly curious over the control logic of the Star pcb (I think it is the same pcb that is used for some lpr systems).
10-11-2007, 06:05 PM #4
Star still have some supplies of the MEV board you just have to ask the right branch or person. Speak to the Telstar department in Glasgow or try one of the branches.
Dunham Bush Chiller Alarm
By Regulator in forum Air ConditioningReplies: 11Last Post: 08-12-2010, 01:42 AM -
fun quiz
By Brian23 in forum New to REReplies: 6Last Post: 02-10-2007, 10:18 PM -
Chiller
By iceman007 in forum Trouble ShootingReplies: 9Last Post: 08-04-2006, 02:48 PM -
Portable chiller shutting down on High Head
By Arkma in forum Trouble ShootingReplies: 10Last Post: 17-06-2005, 01:24 PM