    Question closed loop chiller



    Having problems with a closed loop chiller supplying cooling water for a plastic molding operation. With minimal demand while equipment heats up, coolant (glycol/water) reaches set piont (45 degrees) and maintains. Once production starts, chiller no longer maintains set piont temp even though demand still seems slight. Difference in coolant temp leaving chiller and returning from process is only 4 dgrees. Have checked refrigerant charge, water flow rates, coils are clean. What should superheat range be? Is this a heat transfer problem? Any info appreciated.



  2. #2
    Join Date
    Aug 2001
    Location
    Gold Coast, Australia
    Posts
    600
    Rep Power
    28
    Is the coolant temperature 'bouncing' dramatically, like going from 6 deg. C to 15 deg C. in 5 mins, and pullling down to 6 deg. C. in 3 minutes when the chiller kicks in? If so, you most likely have a coolant flow problem - check the volume of coolant in the system, & make sure it's above the chiller manufacturer's stated minimum. Check that any valves, actuator, etc, are operating correctly.
    Our TEV kit normally works on 6 C at evap. outlet, or 8 - 12 C where we actually have a schrader to connect to, or about 3.5 C if it has an electronic expansion valve. What's the pressure drop through the evaporator? Is that close to the design PD?
    Hope this helps.

  3. #3
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24
    Hi, Bender
    there may not be a problem with the fridge end of the process. Has the system a buffer tank fitted? This would take care of the peak load which could quickly overcome any system which has not been over sized to cope with it.
    TEV superheat should be in the region of 6 Deg C, compressor inlet superheat will be higher than this and is dependant on if a suction liquid heat ex is fitted or not.
    Regards. Andy.

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51
    Hi Bender

    Is it possible to take off one of the water circulating hoses from the tank resorvoir and time the flow into a bucket?

    If you can do this then by weighing the bucket you can determine the actual water flow per second/minute.

    If the delta T is measured and the unit's capcity known then you can calculate everything from then on which will give you the answers to your problem.

    let us know if this is possible. I had a very similar problem just 2 weeks ago!


    Frank

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    Hi Bender,

    Here is the information needed to properly evaluate the system:

    Low side:

    Evap water in temp
    Evap water out temp
    SST (saturated suction temp)
    Suction line temp at evap
    Suction line temp at compressor

    High side:

    Condenser air/water in temp
    Condenser air/water out temp
    SCT (saturated condensing temp)
    Liquid line temp at condenser
    Liquid line temp at metering device

    With these temperatures, we should be able to determine the problem(s).
    Last edited by Gary; 08-12-2002 at 04:58 PM.

  6. #6
    Join Date
    Jul 2001
    Location
    worcester ma
    Age
    60
    Posts
    15
    Rep Power
    0
    hey is the return mixing with the supply check the holding tank.
    have you checked the level of gical it may be to high empty flush system w/descaler and refill w/ polly I would have them depose of the old stuff.

  7. #7
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23
    Hi Tony_Rich

    Your observation regarding high glycol level is very sound advice. I would, as you suggest, dispose of esixting cooling solution, and recharge with the minimal amount of glycol required for freeze protection and corrosion resistance.

    Glycol is a very poor medium for heat transfer.

  8. #8
    Join Date
    Jan 2002
    Location
    Canada
    Posts
    35
    Rep Power
    0
    Hi bender,

    As ask by gary we do need more info.

    Add the flow rate of the secondary coolant, and take the flow rate at different time if you do not have a buffer tank, because the flow rate can change depending on a many equipment you are feeding.

    You said a closed loop therefore you probably do not have a water tank. I hope you have a expansion tank on the secondary coolant.
    Kathleen, P.eng
    www.refri-ozone.com

  9. #9
    Join Date
    Aug 2001
    Location
    Gold Coast, Australia
    Posts
    600
    Rep Power
    28
    Hi Marc

    Good to see you again. That guage is still on my desk, by the way.

    Yeah, I can be sharp at times. Probably comes from having lived mostly on the highveld as a youngster! lol.
    I'm looking forward to seeing Gary's figures too, in case there's more to it. The low flow idea is based on my experience, but until we have some figures, it's a best guess.
    Bender, have you got any more info? Have you solved the problem?

    I'm not surprised at S.A's improving our technology. When I moved back here, I was astonished how far behind the U.K. was! You couldn't even get a statement from a ATM machine! And as a kid, I had a watch that had 4 different games on it - I've never seen anything similar here.
    And the killer is... The SADF's version of the Apache combat helicopter - tougher, meaner, faster, with longer range and bigger payload than the Apache Longbow. Just what you need to get around London! lol

    You're right about the superheat, but we do find that we get some 'high' readings, due to the location of the suction schrader on some of our kit. As a general rule, if it's a screw, it's around 3deg. (as they've got EEV's) and if it's a recip, it's 4-8deg. (TEV control). Obviously that's dependant on load, etc.
    When I was doing pack refrigeration, I was taught to take the superheat across the coil, not back at the compressor. It took a bit of mental gymnastics to get my head around the A/C way of doing it! lol. Oh well, I was a lot greener back then...

    As to what's happening here this year - well, hopefully, this guage will be collected before it gets lost?

    HAPPY NEW YEAR EVERYONE!

Similar Threads

  1. Dunham Bush Chiller Alarm
    By Regulator in forum Air Conditioning
    Replies: 11
    Last Post: 08-12-2010, 01:42 AM
  2. DIY aquarium chiller
    By BarraCuda in forum Technical Discussions
    Replies: 18
    Last Post: 06-10-2010, 11:02 PM
  3. York Screw Chiller How low will it go?????
    By bruceboldy in forum Industrial Compressors
    Replies: 11
    Last Post: 10-08-2007, 10:29 PM
  4. Chiller Fault
    By iceman007 in forum Air Conditioning
    Replies: 2
    Last Post: 13-05-2006, 07:23 PM
  5. thanks & chiller prt. 2
    By bender in forum Trouble Shooting
    Replies: 1
    Last Post: 29-03-2003, 10:31 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •