    condenser cooling water flow



    I have 4 salt water cooled condensers . How would I find out the amount of water, ( gallons per minute ), That I need in each condenser. Hp 80 is the refrigerant in all 4.

    The problem I have is that the old pump is not supplying enough water when it's all running and needs to be replaced



  2. #2
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    517
    Rep Power
    19

    Re: condenser cooling water flow

    The manufacturer of the condenser should be able to tell you what gpm's are required.

  3. #3
    Join Date
    Aug 2007
    Location
    Seattle, WA. USA
    Age
    56
    Posts
    27
    Rep Power
    0

    Re: condenser cooling water flow

    What is the make and model number of the condensers? Also, you say that the old pump is not supplying enough water. Was it sufficient in the past? If it is worn out perhaps all you need is for the condenser pump to be rebuilt.

Similar Threads

  1. pure water from air
    By Lc_shi in forum New Technologies
    Replies: 32
    Last Post: 26-02-2009, 01:25 PM
  2. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  3. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Industrial
    Replies: 5
    Last Post: 14-10-2005, 06:34 PM
  4. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Fundamentals
    Replies: 0
    Last Post: 13-10-2005, 05:14 AM
  5. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •