TEV capacity related to pressure drop
How is the capacity of a thermostatic expansion valve (Danfoss TEN2, orifice 0X in my case) affected when the pressure drop over the valve decreases?
In my small liquid chiller, measurements showed that with a pressure drop of about 9 bars (temp measured in the center of the condenser: 48 degrees C -> 12.5 bar pressure, evaporating at 3.2 bar measured) , the full open capacity of the valve is about 400W. This fits the datasheet, which says 0.5 kW capacity at 8 bar difference.
But, when the pressure drop over the valve is only approximately 4 bars (temp measured in the center of the condenser: 22 degrees C -> 6.1 bar pressure, evap pressure 1.78 bar measured), full open valve capacity drops below 150W. This does not match the datasheet, which says 0.43kW capacity at a pressure drop of 4 bars.
The full open capacity is measured by adding a known amount of heat to the system using a variable voltage source and a resistive heater element, and adding that to the amount of heat leakage determined earlier. The TEV was set to full open by heating the bulb a bit with a hair dryer.
I have about 15K subcooling at the TEV inlet, so flash gas seems not to be a problem. Is the datasheet wrong? (only 0.07kW less capacity when halving the pressure drop seems a bit odd to me). Do I have another problem somewhere?
Similar Threads
-
A question about the pressure drop in coil .
By jackcn in forum FundamentalsReplies: 20Last Post: 13-12-2008, 05:10 PM -
pressure drop of pump return line ammonia
By Moeller in forum FundamentalsReplies: 5Last Post: 04-09-2007, 05:21 AM -
Building a wine cabinet
By Rory in forum Technical DiscussionsReplies: 38Last Post: 13-07-2004, 08:28 PM -
How many small strands needed to equal pipe pressure drop?
By DaBit in forum FundamentalsReplies: 17Last Post: 25-08-2003, 09:56 PM