Results 1 to 8 of 8
Thread: Stal Electronic 700
03-09-2007, 01:08 PM #1
Stal Electronic 700
Hi there,
does anyone have the lay-out or electric scheme?
I have 4 off, mounted on Stal screw compressor units to be rebuilded, but like to know if itis wired okay for testing.
Tnkx.
03-09-2007, 06:48 PM #2
Re: Stal Electronic 700
Hello,
There is no standard scheme for Stalectronic 700, because the application can vary from provision plant units to AC or special applications.
You have to power up the Unit, go to the paramters list to enter all your datas ( Refrigerant, compressor type, etc...), then you have to set setpoint, alarms and so on.
but first you can power up , and go at the bottom of the menu and see what version software it is.
06-09-2007, 04:12 PM #3
For which application are used these compressors? I have few diagrams that You can use as a generic guide line.... And also few parameters list....
Ciao
19-05-2009, 12:45 AM #4
hi
I have r22 s-73 stal compressor ,whit Stal Electronic 700 ,unit fail on stopping pump
why?
in manual position is ok, when chance to auto fail,all pressure and temperature ok
20-05-2009, 09:20 PM #5
Hi Jach, on the S-73 the oil pump is directly on the compressor shaft, is that right? Or is it an electronic failure?
Gerben
21-05-2009, 04:57 AM #6
I have help from stal,now the unit work ok,
thank gerben
22-08-2009, 02:00 PM #7
Hi all!
I have a Stalectronic 700 Electronic control system for SV 10 Compressor Unit. I want use external capacity control compressor via an analog input (AI8) and a digital input (DI4) in remote operating mode, but not working. Please help me setup in Stalectronic 700. Thanks.
07-10-2010, 06:33 AM #8
Stal Screw Compressor R5-mkii 100kw
By REFSOO in forum Trouble ShootingReplies: 1Last Post: 20-01-2007, 01:09 AM -
Stal Problems
By NH3LVR in forum Industrial CompressorsReplies: 2Last Post: 16-09-2006, 11:08 AM -
Help with new electronic refrigerator controller !
By EngiGal in forum New TechnologiesReplies: 17Last Post: 08-04-2006, 07:39 PM -
Electronic Controls
By Bones in forum Supermarket RefrigerationReplies: 16Last Post: 04-04-2004, 06:52 AM -
Oversizing EXV electronic expansion valve
By aygul in forum Technical DiscussionsReplies: 5Last Post: 20-11-2003, 01:00 PM