    Volume of circulating receiver



    Please advise me - how to calculate needed volume of circulating receiver?



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Volume of circulating receiver

    I am assuming you mean a receiver that has refrigerant pumps to circulate the liquid refrigerant...

    The size is based on several critical elements:
    1. The volume of liquid to be stored
    2. The maximum liquid level desired
    3. The volume needed for separating liquid from vapor before the compressor
    The usual method for a horizontal is to fix the vessel volume at 1/2 full. In this case you use the top half of the vessel for the liquid/vapor separation.

    The volume of liquid to be stored determines how much volume you need below the maximum liquid level of 1/2 of the vessel diameter.

    In addition you need a minimum liquid level to ensure the refrigerant pumps can prime and operate.

    These are the basic fundamentals for either a vertical or horizontal vessel.

    This is a complex subject and will stretch over many replies from others also. This is just a starting point.
    If all else fails, ask for help.


  3. #3
    Join Date
    Apr 2005
    Location
    Moscow
    Age
    48
    Posts
    20
    Rep Power
    0

    Re: Volume of circulating receiver

    US Iceman

    Thanks for you reply. Yes i wrote about receiver that has refrigerant pumps. I think it`s a very interesting subject too. From one side it`s very simlpe, but from other it`s have some features. How do you calculate needed volume for calculating receiver?

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Volume of circulating receiver

    The more difficult problem is estimating the volume of the evaporators that will be in defrost at any one time. If the evaporators are using hot gas defrost, the volume of liquid in the coils has to be stored in the receiver during defrost. This is what I call the surge volume.

    This volume occupies the area between the normal operating liquid level and the maximum liquid level (before the compressors are de-energized due to high liquid levels).
    If all else fails, ask for help.


  5. #5
    Join Date
    Apr 2005
    Location
    Moscow
    Age
    48
    Posts
    20
    Rep Power
    0

    Re: Volume of circulating receiver

    Quote Originally Posted by US Iceman View Post
    The more difficult problem is estimating the volume of the evaporators that will be in defrost at any one time. If the evaporators are using hot gas defrost, the volume of liquid in the coils has to be stored in the receiver during defrost. This is what I call the surge volume.

    This volume occupies the area between the normal operating liquid level and the maximum liquid level (before the compressors are de-energized due to high liquid levels).
    But in this case you can prohibit the simultaneous defrost. What do think about retention time?

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Volume of circulating receiver

    I think the pump retention time should be based on the liquid volume to re-fill the evaporators after defrost. However, you also have the surge volume from the evaporator defrost liquid (and pumpdown) providing a lot of liquid in the vessel.

    I have seen some recommendations that say you need at least five minutes of retention time for the pumping rate.

    As a point of argument I would say it is more important to make sure the liquid make-up supply can maintain the minimum pump liquid level during normal operation.
    If all else fails, ask for help.


Similar Threads

  1. Receiver! Needed or not
    By The MG Pony in forum Fundamentals
    Replies: 4
    Last Post: 22-08-2007, 08:51 PM
  2. liquid receiver low level alarm
    By racknovice in forum Supermarket Refrigeration
    Replies: 8
    Last Post: 18-08-2007, 06:53 PM
  3. Condenser outlet lower than receiver inlet.
    By Pawel_Wisnik in forum Technical Discussions
    Replies: 7
    Last Post: 20-02-2007, 09:18 AM
  4. Volume ratio selection
    By rosetennis in forum Industrial Compressors
    Replies: 4
    Last Post: 14-07-2006, 02:10 AM
  5. Starting a compressor, and receiver questions.
    By DaBit in forum Technical Speculations
    Replies: 9
    Last Post: 24-08-2002, 12:37 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •