help needed ,
Hello guys ,
i have just fitted a new comp on a domestic fridge on r134a, 130g put in , what would you think is a reasonable ruuning pressure?
when i added the gas and turned compressor on , it pulled my gauge down into a vac as if i had front seated the service valve ?? its on a capillary device which coming from air con back ground i have not really worked on ,
i changed the gas dryer , could there be a blockage on the capillary when i re-inserted it ?
after re-fitting the dryer , i was getting 0.6bar low side pressure and about 12bar high side ??
any help is much appriciated
thanks alan
-
31-08-2007, 07:42 AM #2
Re: help needed ,
Check out the phase connection accuracy in your compressor.
-
31-08-2007, 08:11 AM #3
Re: help needed ,
Is the compressor bigger than the old one, if it is that could be the problem, if it is an exact size for size match the chances are that you have blocked the capillary with solder.
-
31-08-2007, 08:01 PM #4
Re: help needed ,
thanks for your help guys ,
-
01-09-2007, 12:52 AM #5
Re: help needed ,
-
02-09-2007, 06:44 PM #6
-
02-09-2007, 09:35 PM #7
-
03-09-2007, 12:46 AM #8
-
04-09-2007, 01:43 PM #9
Re: help needed ,
Hi,
The Normal runnig back pressure foa a domestic unit is
5 - 8 PSI
-
04-09-2007, 06:11 PM #10
Re: help needed ,
Fridges these days are dodgey things at best. They are designed to run at low presure, high TD because humidity isn't considered anymore. This setup means minimal evap size and refrig charge.
First of all, did this cabinet have a critical charge labelled on it?
If not, it's best to find that out from the manufacturer directly. Otherwise the best bet when charging is to disconnect the evap fan and charge until the suction line frosts back to the heat exchanger (if fitted) or compressor.
If there's a blockage in the capillary it usualy runs in a vacuum on SP, plus you'll never get liquid frosting to the HX/compressor with the fan off (which is why it's a handy way to charge capillary systems.)Last edited by paul_h; 04-09-2007 at 06:14 PM.
-
04-12-2007, 01:30 PM #11
-
05-12-2007, 12:13 PM #12
Re: help needed ,
Domestic refrigeration back pressures are normally left running at 5 Psi.
From what you are saying it would seem that there may be a blockage at the evaporator plate end (this is not unusual with domestics). I would suggest that you refit a new drier whilst purging the system with a small amount of N2,if after you have fully vacc'd the system and charged it if you are still getting a negitive pressure then it may be time to replace the cabinet.
-
03-03-2008, 09:32 PM #13
Re: help needed ,
thanks to you all
Similar Threads
-
Autocascade refrigeration system: design verification needed
By DaBit in forum Technical SpeculationsReplies: 3Last Post: 07-02-2010, 07:48 AM -
Carrier 40GKX028 service manual needed
By Ireland in forum Air ConditioningReplies: 6Last Post: 08-02-2007, 07:06 PM -
UK Help needed
By Air-Con Man in forum Air ConditioningReplies: 6Last Post: 23-01-2007, 08:57 AM -
How many small strands needed to equal pipe pressure drop?
By DaBit in forum FundamentalsReplies: 17Last Post: 25-08-2003, 09:56 PM -
Help Needed Mitsi MSC07RV/MUH-07RV
By Latte in forum Air ConditioningReplies: 2Last Post: 24-08-2003, 03:00 PM