    help needed ,



    Hello guys ,

    i have just fitted a new comp on a domestic fridge on r134a, 130g put in , what would you think is a reasonable ruuning pressure?

    when i added the gas and turned compressor on , it pulled my gauge down into a vac as if i had front seated the service valve ?? its on a capillary device which coming from air con back ground i have not really worked on ,

    i changed the gas dryer , could there be a blockage on the capillary when i re-inserted it ?

    after re-fitting the dryer , i was getting 0.6bar low side pressure and about 12bar high side ??

    any help is much appriciated

    thanks alan



  2. #2
    Join Date
    May 2007
    Location
    Moscow
    Age
    40
    Posts
    82
    Rep Power
    18

    Re: help needed ,

    Check out the phase connection accuracy in your compressor.

  3. #3
    Join Date
    Jun 2005
    Location
    Stoke on Trent
    Age
    62
    Posts
    588
    Rep Power
    19

    Re: help needed ,

    Is the compressor bigger than the old one, if it is that could be the problem, if it is an exact size for size match the chances are that you have blocked the capillary with solder.

  4. #4
    Join Date
    Jul 2007
    Location
    england
    Age
    44
    Posts
    98
    Rep Power
    17

    Re: help needed ,

    thanks for your help guys ,

  5. #5
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: help needed ,

    Quote Originally Posted by wilks View Post
    thanks for your help guys ,

    How are you measuring the pressures because domestics have no access to the discharge.
    .5 of a bar is not untoward for the suction of a domestic fridge.
    The cappilary line could be blocked or partialy blocked, but if it is running what are the temps in the fridge?

    taz.

  6. #6
    Join Date
    Jul 2007
    Location
    england
    Age
    44
    Posts
    98
    Rep Power
    17

    Re: help needed ,

    Quote Originally Posted by taz24 View Post
    How are you measuring the pressures because domestics have no access to the discharge.
    .5 of a bar is not untoward for the suction of a domestic fridge.
    The cappilary line could be blocked or partialy blocked, but if it is running what are the temps in the fridge?

    taz.
    hi taz

    its a drug fridge at a hospital , it has a access port on the gas dryer ,

    it actually gets down to 3oC so its working , it a medium size fridge , do you think that 150g is enough??

  7. #7
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: help needed ,

    Quote Originally Posted by wilks View Post
    hi taz

    its a drug fridge at a hospital , it has a access port on the gas dryer ,

    it actually gets down to 3oC so its working , it a medium size fridge , do you think that 150g is enough??
    So its approx the size of a domestic fridge.
    150g seems a reasonable figure but the temps and the pressures will prove it to be ok.
    If its down to temp then let it run and see what happens.
    Cheers taz.

  8. #8
    Join Date
    Jul 2007
    Location
    england
    Age
    44
    Posts
    98
    Rep Power
    17

    Re: help needed ,

    Quote Originally Posted by taz24 View Post
    So its approx the size of a domestic fridge.
    150g seems a reasonable figure but the temps and the pressures will prove it to be ok.
    If its down to temp then let it run and see what happens.
    Cheers taz.
    thanks taz

  9. #9
    Join Date
    Feb 2005
    Location
    United Kingdom
    Age
    73
    Posts
    18
    Rep Power
    0

    Re: help needed ,

    Hi,
    The Normal runnig back pressure foa a domestic unit is
    5 - 8 PSI

  10. #10
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: help needed ,

    Fridges these days are dodgey things at best. They are designed to run at low presure, high TD because humidity isn't considered anymore. This setup means minimal evap size and refrig charge.
    First of all, did this cabinet have a critical charge labelled on it?
    If not, it's best to find that out from the manufacturer directly. Otherwise the best bet when charging is to disconnect the evap fan and charge until the suction line frosts back to the heat exchanger (if fitted) or compressor.
    If there's a blockage in the capillary it usualy runs in a vacuum on SP, plus you'll never get liquid frosting to the HX/compressor with the fan off (which is why it's a handy way to charge capillary systems.)
    Last edited by paul_h; 04-09-2007 at 06:14 PM.

  11. #11
    Join Date
    Jan 2007
    Location
    ITALY
    Age
    63
    Posts
    21
    Rep Power
    0

    Re: help needed ,

    Quote Originally Posted by wilks View Post
    Hello guys ,

    i have just fitted a new comp on a domestic fridge on r134a, 130g put in , what would you think is a reasonable ruuning pressure?

    when i added the gas and turned compressor on , it pulled my gauge down into a vac as if i had front seated the service valve ?? its on a capillary device which coming from air con back ground i have not really worked on ,

    i changed the gas dryer , could there be a blockage on the capillary when i re-inserted it ?

    after re-fitting the dryer , i was getting 0.6bar low side pressure and about 12bar high side ??

    any help is much appriciated

    thanks alan
    NOW YOU DON,T HAVE TO WORRY ABOUT THIS, BECAUSE MOST OF DOMESTIC FRIDGES WITH R 12 AND R 134A WORKS ALMOST IN VAC. R 134A AT -30 IS ALMOST VAC. YOU NEED MORE EXPIRIENCE TO WORK ON DOMESTIC FRIDGES. THEY LOOK SIMPLE BUT THEY ARE NOT. SEE YOU

  12. #12
    Join Date
    Feb 2005
    Location
    United Kingdom
    Age
    73
    Posts
    18
    Rep Power
    0

    Re: help needed ,

    Domestic refrigeration back pressures are normally left running at 5 Psi.
    From what you are saying it would seem that there may be a blockage at the evaporator plate end (this is not unusual with domestics). I would suggest that you refit a new drier whilst purging the system with a small amount of N2,if after you have fully vacc'd the system and charged it if you are still getting a negitive pressure then it may be time to replace the cabinet.

  13. #13
    Join Date
    Mar 2008
    Location
    uk
    Posts
    24
    Rep Power
    0

    Re: help needed ,

    thanks to you all

Similar Threads

  1. Autocascade refrigeration system: design verification needed
    By DaBit in forum Technical Speculations
    Replies: 3
    Last Post: 07-02-2010, 07:48 AM
  2. Carrier 40GKX028 service manual needed
    By Ireland in forum Air Conditioning
    Replies: 6
    Last Post: 08-02-2007, 07:06 PM
  3. UK Help needed
    By Air-Con Man in forum Air Conditioning
    Replies: 6
    Last Post: 23-01-2007, 08:57 AM
  4. Replies: 17
    Last Post: 25-08-2003, 09:56 PM
  5. Help Needed Mitsi MSC07RV/MUH-07RV
    By Latte in forum Air Conditioning
    Replies: 2
    Last Post: 24-08-2003, 03:00 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •