    Thumb rule for belt driven compressor - Power loss



    We are comparing direct drive compressor system against Belt driven compressor system.

    What is the thumb rule figure for loss due to belt driven system ( is it 2 to 3 %)



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Thumb rule for belt driven compressor - Power loss

    That is a reasonable percentage to use for belt drive compressors. You do need to find out if the compressor ratings include this loss, or if you need to correct for belt drive losses yourself.
    If all else fails, ask for help.


  3. #3
    Join Date
    Sep 2007
    Location
    New Zealand
    Age
    79
    Posts
    54
    Rep Power
    17

    Re: Thumb rule for belt driven compressor - Power loss

    I have incorporated belt drives in many installations on reciprocating compressors of varying sizes with little problems and have proved the transmission to be reasonably efficient and reliable. The correct selection for the Job being considered is paramount.
    In general I have found the efficiencies to be in the rage between 95 to 98 % but this is hard to determine . The Input power can be determined fairly easily but the HP input to the driven device at best is estimated.
    If you check out the Web or Google "Gates" Will give a back ground to this matter of belt drive efficiencies.

  4. #4
    Join Date
    May 2007
    Location
    India
    Posts
    695
    Rep Power
    17

    Re: Thumb rule for belt driven compressor - Power loss

    I know that it is difficult to determne the exact losses, but at the same time, we have to put in figures for the sake of consultants & I think Mr. John's Figures do match with What I knew. Many thanks

  5. #5
    Join Date
    May 2007
    Location
    India
    Posts
    695
    Rep Power
    17

    Re: Thumb rule for belt driven compressor - Power loss

    Dear Mr. John,

    The client has atleast taken up the figures vey seriously & ofcourse he shall cross check with this own sources. But at the same , he said that the data furnished to him by all the concerned like consultants etc was worng on this score. We are now very much in the race to get this order, though it could be delayed for the time being. Your answer at the right time helped us a lot.

Similar Threads

  1. 404A head pressure to ambient rule of thumb
    By kengineering in forum Refrigerants
    Replies: 22
    Last Post: 08-05-2007, 10:40 PM
  2. Rule of Thumb on Refrigerant Amount
    By rickmor in forum Refrigerants
    Replies: 7
    Last Post: 19-12-2005, 12:18 PM
  3. condensing temp rule of thumb
    By angryk in forum Fundamentals
    Replies: 8
    Last Post: 14-03-2003, 05:00 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •