    Jun 2007
    South Africa
    80
    Ammonia Plant vs Chiler units
    I need the opinions and experience of the masses:
    I require glycol spplied at -10C and 0C for air coolers loacted in various rooms.
    With classical industrial refrigeration, I can achived this using Ammonia, LP veesels, compressors, condensers, pumps etc..
    However, chiller units to can produce chiled glycol (even at -10C, so the manufacturer said). These chiller units also have pumps as pert of teh packakge. Redunday wrt compressors would be easy to achieved.
    My refrigeration heat load is quite low;
    a) -10C glycol supply for 300KW.
    b) 0C glycol supply for 600KW.
    Additionally - would screws or recips be better??
    Maybea similar excesie had been carried out by you. What are the opinions.
    Aug 2005
    5,302
    Re: Ammonia Plant vs Chiler units
    My preference would be to use a small ammonia central system operating at two evaporating temperatures. Each temperature level could have at least two compressors, plus an additional compressor connected to operate off of either temperature level (as a swing compressor).
    So you would have 2 compressors for the -10°C load & 2 compressors for the 0°C load, with one compressor capable of operating off of either temperature level.
    I like recip. compressors. Their part load efficiency is much better than screws and they are easier to work on.
    I think I would look at some flooded plate heat exchangers and an evaporative condenser which sufficient reserve capacity for low condensing temperatures.
    The refrigeration system is the easy part. How are you planning on defrosting the glycol coils when required?
    Jun 2007
    South Africa
    80
    Hi - thanks for the reply
    I agree with your thoughts on the Ammonia plant - what I need to perform is a Cost Benefit Analysis of the 2 options, and a plantroom comparison. The chiller is a complete unit, no plantroom required, using possibly R134a (They dont make them in R22 - the site is in a developing country)
    My thoughts on the defrost were Electric (I could use Hot Gas - however, the number of coils will be low and I wuld have to add anothe PHe and a set of pumps)
    So much work - so little time...
    Aug 2007
    42
    135
    Halls have started doing chillers on ammonia with either air cooled or Evap condensers, as have grenco. Everything is on inverters. Bit pricey but they are very efficent.
    Jun 2007
    South Africa
    80
    Thanks - I could not find anny brochures on the website. Do you know where I can get some.
    Jan 2006
    Croatia
    68
    2,261
    31
    Hi, Samiam
    I have to agree with US Iceman..in all.
    Quote Originally Posted by samiam View Post
    If you want low first installation costs then you should go with chillers...as you said: it is in one "developing country" why not "help them to save some money" and install cheap crap
    If you want low running cost and long time (20-30years) running plant then...install industrial ammonia plant, to leave something worth behind you...
    No need any "Cost Benefit Analysis"....believe me.
    Best regards, Josip
    Feb 2008
    Napa, CA
    54
    33
    First your USA loads are:
    85 tons and 170 tons but I didn't see any actual room temps...
    I definitely would look at a built up system rather than a "chiller" package of any type.
    Advantages: (if designed right)
    Defrost heat is free on built-up systems
    No parasitic loads of glycol pumps
    Less things to go wrong
    No secondary heat exchange increasing efficiency
    Ease of multiple evap temps
    Best ROI (again if designed properly, built for your facility, in your geographical location, with your energy costs)
    As far as ammonia vs a halocarbon. Either is a preference. Contreary to most thought you can have a more efficient R-22 system than an NH3 system depending on design...
    Never go with a packaged system. Chillers are by name inefficent they are designed to Chill water not your load.
  1. ammonia refrigeration system
    Last Post: 25-06-2010, 10:03 AM
  2. Oil removal from Ammonia plant
    By psrao in forum NH3
    Last Post: 23-03-2007, 09:59 PM
  3. Ammonia and CO2 reactor
    By gwapa in forum NH3
    Last Post: 07-01-2007, 04:50 PM
  4. Ammonia Plant
    By kevinxt in forum NH3
    Last Post: 04-01-2007, 08:54 AM
  5. New Ammonia Certification in United States
    By JerrydNH3 in forum NH3
    Last Post: 15-08-2006, 03:10 PM