Results 1 to 10 of 10
Thread: TXVs with MOP
    Jul 2007
    Indonesia
    38
    30
    Wink TXVs with MOP
    Hi all,
    Its beginner starting to find out basics of refrigeration again...
    I want to know from the practical side, when do we need to use TXV with MOP??
    Nov 2005
    belgium
    61
    Re: TXVs with MOP
    Hello,
    you have to use a MOP for protection of the compressor.
    MOP -10°C, the valve opens when the suction gas pressure is lower than -10°C.
    When you have a freezer, after a defrost, the gas pressure can be to high and can break the compressor.
    MOP hold the pressure and open when the pressure is low and safe enough for the compressor.
    Used in airco has the same function.
    Hope i helped you a little.
    Jul 2007
    Indonesia
    38
    30
    Re: TXVs with MOP
    Hallo Nando...
    What do u mean with "MOP hold the pressure" ?
    So the valve is completely closed when the low side pressure is too high? My thought was the valve will be fully open if the evaporator pressure is high
    Aug 2007
    Surabaya
    42
    Re: TXVs with MOP
    Hallo Tante Ian, you can find the details explanation of MOP in Handbook of HVAC Shan K Wang.
    Moscow
    40
    82
    Re: TXVs with MOP
    Hi, Herdian. Check this linc of Alco Controls http://www.astra.dp.ua/upload/do/alc...n_TI__3524.pdf
    Nov 2005
    belgium
    61
    Re: TXVs with MOP
    Hello Herdian,
    When the pressure is to high, the valve will open a little bit, that time the evaperator pressure is lower than the MOP point.
    When the temp. in the room gets down, the evaperator temp. gets lower, the temp. on the bulb from the valve gets lower, the valve opens more. This untill the evaporator pressure is same the MOP point, than the valve is completly open. Than the valve begins to work like normall.
    Valve MOP -10°C: when the temp. on the bulb is 0°C, the valve is a little bit open, from -10°C on the bulb, the valve is 100% open and begins to work normall.
    Oct 2003
    5,630
    34
    Re: TXVs with MOP
    Quote Originally Posted by Cewek ITS View Post
    I don't have that book Uncle Sewec, so what to do now?
    Jul 2007
    Indonesia
    38
    30
    Re: TXVs with MOP
    OK thank u Nando and DVaider, now i almost completely understand on how this kind of TXV works.
    But i have minimum experience on field...so, after a defrost the evaporator pressure will be high, actually what kind of action does this TXV provides to prevent overload of compressor [how does the evaporator can be lowered on its pressure before the compressor starts to operate again]?
    Aug 2005
    5,302
    Re: TXVs with MOP
    See the text on page 7 of the link. Look under "Air Conditioning & Heat Pump Applications".
    http://www.sporlan.com/10-9.pdf
    Maybe this will provide sufficient information for your questions...
    Jul 2007
    Indonesia
    38
    30
    Re: TXVs with MOP
    Thanks US Iceman...read, read and read again...
    I wonder when will i have a chance to practice it...i think my chance is small...too much expert which is men...
  1. SERVO TXVs
    By T_Schmidt in forum New Technologies
    Last Post: 11-06-2007, 08:44 PM
  2. Basics of TXV's
    By US Iceman in forum Fundamentals
    Last Post: 21-05-2007, 03:27 PM
  3. TXV's
    By JerrydNH3 in forum NH3
    Last Post: 03-08-2006, 10:54 PM
  4. Help geting more info on some TXVs
    By The MG Pony in forum Chit Chat & Service Stories
    Last Post: 07-07-2006, 05:47 PM
  5. TXV's and LST compressors
    Last Post: 18-06-2002, 02:27 PM