    Wink TXVs with MOP



    Hi all,
    Its beginner starting to find out basics of refrigeration again...
    I want to know from the practical side, when do we need to use TXV with MOP??



  2. #2
    Join Date
    Nov 2005
    Location
    belgium
    Posts
    61
    Rep Power
    0

    Re: TXVs with MOP

    Hello,
    you have to use a MOP for protection of the compressor.
    MOP -10°C, the valve opens when the suction gas pressure is lower than -10°C.
    When you have a freezer, after a defrost, the gas pressure can be to high and can break the compressor.
    MOP hold the pressure and open when the pressure is low and safe enough for the compressor.
    Used in airco has the same function.
    Hope i helped you a little.

  3. #3
    Join Date
    Jul 2007
    Location
    Indonesia
    Age
    38
    Posts
    30
    Rep Power
    0

    Re: TXVs with MOP

    Hallo Nando...
    What do u mean with "MOP hold the pressure" ?
    So the valve is completely closed when the low side pressure is too high? My thought was the valve will be fully open if the evaporator pressure is high

  4. #4
    Join Date
    Aug 2007
    Location
    Surabaya
    Age
    42
    Posts
    18
    Rep Power
    0

    Re: TXVs with MOP

    Hallo Tante Ian, you can find the details explanation of MOP in Handbook of HVAC Shan K Wang.

  5. #5
    Join Date
    May 2007
    Location
    Moscow
    Age
    40
    Posts
    82
    Rep Power
    17

    Re: TXVs with MOP

    Hi, Herdian. Check this linc of Alco Controls http://www.astra.dp.ua/upload/do/alc...n_TI__3524.pdf

  6. #6
    Join Date
    Nov 2005
    Location
    belgium
    Posts
    61
    Rep Power
    0

    Re: TXVs with MOP

    Hello Herdian,
    When the pressure is to high, the valve will open a little bit, that time the evaperator pressure is lower than the MOP point.
    When the temp. in the room gets down, the evaperator temp. gets lower, the temp. on the bulb from the valve gets lower, the valve opens more. This untill the evaporator pressure is same the MOP point, than the valve is completly open. Than the valve begins to work like normall.
    Valve MOP -10°C: when the temp. on the bulb is 0°C, the valve is a little bit open, from -10°C on the bulb, the valve is 100% open and begins to work normall.

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: TXVs with MOP

    Quote Originally Posted by Cewek ITS View Post
    Hallo Tante Ian, you can find the details explanation of MOP in Handbook of HVAC Shan K Wang.
    I don't have that book Uncle Sewec, so what to do now?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  8. #8
    Join Date
    Jul 2007
    Location
    Indonesia
    Age
    38
    Posts
    30
    Rep Power
    0

    Re: TXVs with MOP

    OK thank u Nando and DVaider, now i almost completely understand on how this kind of TXV works.
    But i have minimum experience on field...so, after a defrost the evaporator pressure will be high, actually what kind of action does this TXV provides to prevent overload of compressor [how does the evaporator can be lowered on its pressure before the compressor starts to operate again]?

  9. #9
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: TXVs with MOP

    See the text on page 7 of the link. Look under "Air Conditioning & Heat Pump Applications".

    http://www.sporlan.com/10-9.pdf

    Maybe this will provide sufficient information for your questions...
    If all else fails, ask for help.


  10. #10
    Join Date
    Jul 2007
    Location
    Indonesia
    Age
    38
    Posts
    30
    Rep Power
    0

    Re: TXVs with MOP

    Thanks US Iceman...read, read and read again...
    I wonder when will i have a chance to practice it...i think my chance is small...too much expert which is men...

Similar Threads

  1. SERVO TXVs
    By T_Schmidt in forum New Technologies
    Replies: 2
    Last Post: 11-06-2007, 08:44 PM
  2. Basics of TXV's
    By US Iceman in forum Fundamentals
    Replies: 5
    Last Post: 21-05-2007, 03:27 PM
  3. TXV's
    By JerrydNH3 in forum NH3
    Replies: 1
    Last Post: 03-08-2006, 10:54 PM
  4. Help geting more info on some TXVs
    By The MG Pony in forum Chit Chat & Service Stories
    Replies: 5
    Last Post: 07-07-2006, 05:47 PM
  5. TXV's and LST compressors
    By DaBit in forum Technical Speculations
    Replies: 32
    Last Post: 18-06-2002, 02:27 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •