    Oops installed 134A cond unit with a 404 TXV



    While on the road I found that one of my guys hooked a 134a condensing unit to a remote evaporator with a 404 valve. It was then evacuated, charged with 134A and ran. This is all i know. I can't wait to find out more as this is holiday week and then I start vacation so I woun't find out for awhile.
    1) What is likely to have happened
    2) Are there any long term effects on the TXV after the proper unit and gas is used.
    3) It what ways are condensig units different for the different refrigerants.
    Ken
    Last edited by kengineering; 02-09-2007 at 10:52 PM. Reason: grammer



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Oops installed 134A cond unit with a 404 TXV

    The only difference would have been in how well the TXV regulated.
    If the compressor survived then you shouldn't have any problems.

  3. #3
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Oops installed 134A cond unit with a 404 TXV

    Quote Originally Posted by kengineering View Post
    1) What is likely to have happened
    2) Are there any long term effects on the TXV after the proper unit and gas is used.
    3) It what ways are condensig units different for the different refrigerants.
    Ken

    It should not have a detrimental effect as long as liquid does not flood back to the comp.

    Just think how they work? They are only glorified holes that have a bit of control.
    It will not perform the same but I don't think that it is a big deal.
    Your guy should pump the system down and just change the valve.
    15mins and all will be back to normal.

    Cheers taz.

  4. #4
    Join Date
    Dec 2005
    Location
    USA
    Posts
    222
    Rep Power
    20

    Re: Oops installed 134A cond unit with a 404 TXV

    Yea I figured the glory hole thing but wasn't sure it would flood. I thought , at the higher operating pressure the valve works with, the evap would starve? Ken

Similar Threads

  1. Problem with ducted Daikin
    By jutty in forum Trouble Shooting
    Replies: 8
    Last Post: 23-07-2007, 05:34 AM
  2. Off-line Mitsi VRF leaks!
    By sinewave in forum Air Conditioning
    Replies: 8
    Last Post: 05-06-2007, 11:18 PM
  3. Wiring diagram for Prestcold Cond Unit
    By Abe in forum Commercial
    Replies: 2
    Last Post: 24-08-2005, 09:27 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •