    Re-charge heat pump R410a



    Hello all,

    I have a R410a split system heat pump that requires a full recharge, the service valve is on the LP Vapor Side. I know that R410a has to be charged in its liquid state to maintain the blend but im cautious of possible damage to the compressor, I intend to add refrigerant slowly throttling the valve to vaporise the liquid in the lines. I dont have to hand an atomiser/safety charger, can anyone who has had experience with these systems share there methods also the system charge is 1.5Kg is there a recommended point when i should envoke the compressor?

    Your help is greatly appreciated!



  2. #2
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Re-charge heat pump R410a

    Evacuate the system, then liquid charge through the suction port when the system isn't running. When the system is in a vacuum, I have no problem getting 3.5kg into these systems.
    Wait 5-10 min before running the compressor.

  3. #3
    Join Date
    Apr 2007
    Location
    lancashire england
    Age
    64
    Posts
    36
    Rep Power
    0

    Re: Re-charge heat pump R410a

    vac it out bomb charge it and weigh the charge in then let the liquid boil off and hey presto

  4. #4
    Join Date
    May 2007
    Location
    NC
    Posts
    262
    Rep Power
    17

    Re: Re-charge heat pump R410a

    Did the system run in a vacuum? If so you may need to do some more work than just recharge or else you get the green slime if to much moisture entered the system while it was pumping in a vacuumor pumping straight atmospheric air through the system. If you know how long it ran without refrigerant that would be a big help also.

  5. #5
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: Re-charge heat pump R410a

    BigJon brings in a good point! If you suspect it ever ran in a vac I'd toss ina good big Filter dryer to ensure a good dry system.

  6. #6
    Join Date
    May 2007
    Location
    NC
    Posts
    262
    Rep Power
    17

    Re: Re-charge heat pump R410a

    Filter dryer always goes in with 410a if the system is opened. I was referring to the poe oil absorbing moisture. You may need to change out the oil and then install a filter dryer just to be safe. If there is enough moisture in the system you can charge it correctly and come back later and the moisture in the system will start to turn the oil and ref. into a green sludge. You have some room to play but if this thing ran for a week like this I would change the oil and start over fresh with dryers and virgin ref.

Similar Threads

  1. DIY heat pump 12kW
    By kimusabi in forum Fundamentals
    Replies: 11
    Last Post: 17-10-2009, 07:50 PM
  2. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  3. Will this heat pump work?
    By goodguy in forum Heat Pumps
    Replies: 7
    Last Post: 08-03-2008, 04:14 PM
  4. swimming pool heat pump
    By Andy AC in forum The Trail of Tears
    Replies: 8
    Last Post: 26-08-2007, 04:02 PM
  5. heat pump capacity adjust
    By Lc_shi in forum Fundamentals
    Replies: 5
    Last Post: 14-02-2006, 07:32 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •