22-08-2007, 05:36 PM #1
I Have A Copelametic Model Kam2-0075-1aa. Was Working Fine Now Every Time You Start It The Start Capacitor Smokes And Blows. Not Sure Why Nothing Changed. Thanks For Any Help
22-08-2007, 07:09 PM #2
Re: Start Capacitors Blows
Stop turning it on, you will bust it. Sounds like it needs a new start capacitor, or better still all new start electrics (relay, run and start capacitors) assuming its not a psc (permanent split capacitor) compressor. when you've fitted these run it up with a amp meter to check the start and run current against the details on the lable on the compressor.
Jon
22-08-2007, 07:43 PM #3
Have you checked the start winding resistance against what it's supposed to be?
Have you checked the acutal capacitor for correct micro-farads capacitance?
22-08-2007, 11:31 PM #4
JUJU
I Assume that this compressor has a Voltage operated Start relay. Sounds like this has failed and start cap is permanently "in circuit".....it normally switches out of circuit when start winding volts reach > than line volts.
12-09-2007, 10:10 PM #5
sounds like the relay to me. the start winding is being hed in all the time and this is what is causing your capacitors to blow up after a few seconds. dont they stink when they do that and it dont half make you jump!!
14-09-2007, 03:09 PM #6
sounds like start relay is staying in for too long.
this could be caused by faulty relay or low resistance on start windings, causing too much EMF and may be holding in the relay.. mainly with current coil type relays.
another thing.. did the original capacitor have a bleed resistor? important if the compressor is using a potential type relay...
16-09-2007, 10:12 AM #7
New set of electrics, relay problem.
17-09-2007, 08:10 PM #8
hi guys could be that you are dropping a neutral on the power supply
Hard start, Soft Start, Inverter???
By tkc100 in forum FundamentalsReplies: 9Last Post: 28-07-2007, 09:47 PM -
Hot start problem on VRV REYQ14M7W1B
By cool#9 in forum Air ConditioningReplies: 9Last Post: 20-04-2007, 08:09 PM -
how can i start ?
By cruzeiros in forum Legal-Business-MarketingReplies: 5Last Post: 30-06-2006, 12:09 PM -
Capacitor Start Motor
By bryan2392 in forum ElectricalReplies: 7Last Post: 27-01-2006, 07:17 PM -
Capacitors
By Abe in forum Trouble ShootingReplies: 5Last Post: 13-01-2002, 03:08 PM