20-08-2007, 05:24 PM #1
R12 drop-ins
Hi All, I need to replace a compressor AJ4492A and have been told a CAJ4492A will do the job, does the C stand for Capacitor?? and will it do the job? the next question is this degreaser ran on R12 now which drop-in is the correct one to use, I have been told isceon 49,134a, 413a, R406a,R401a,R414b?
Can anyone clarify?
Regards
AZA
-
20-08-2007, 07:02 PM #2
Re: R12 drop-ins
49 is verry succesfull option, 401a second for med temp, R-401b is low tem.
-
20-08-2007, 07:44 PM #3
Re: R12 drop-ins
R409/49
Regards PP
-
20-08-2007, 08:02 PM #4
Re: R12 drop-ins
Hi Aza
C or no letter = single phase eg AJ/CAJ etc
T = three phase eg TAJ,TAG,TAN etc
JonLast edited by monkey spanners; 20-08-2007 at 08:05 PM.
-
20-08-2007, 08:32 PM #5
Re: R12 drop-ins
I'd go for R413a never had any problems.
Grumpy men live longer
-
20-08-2007, 08:39 PM #6
Re: R12 drop-ins
Thanks for the help guys
-
04-09-2007, 01:57 PM #7
Re: R12 drop-ins - why no 414 ?
Is there some reason I should Not be using R-414B as a drop in for R-12 ?
PHM
------------
-
05-09-2007, 10:11 AM #8
Re: R12 drop-ins
Hi AZA,
yes C does basically stand for capacitor start...High Starting Torque.
ECM
-
05-09-2007, 03:47 PM #9
Re: R12 drop-ins
hi i have just put in 134a in a bottle chiller and its still going 5 weeks later happy days.
-
05-09-2007, 08:20 PM #10
Re: R12 drop-ins - why no 414 ?
ICOR seems to be hated , because the sales rep, in this forum and the other, but, I have had great success in the medium temp applications. Not so good in low temp, just do to the fact that to obtain a solid column of liquid to the txv you end up with really high subcooling. Seems to throw the unit off when it has a big load.
-
08-09-2007, 02:37 AM #11
Re: R12 drop-ins
The guys at my shop are sold on 420a as the only r12 replacement in most systems. I have to admit it does work well but flooding is always a concern.
-
22-10-2007, 01:44 AM #12
Re: R12 drop-ins
rs24?.....im using it...seems to work ok?
-
02-01-2008, 05:44 AM #13
Re: R12 drop-ins
I have been using 414b for R12 and 134a systems for several years now with absolutly no problems. in a 12 system you only charge to 80% of design and for a 134a system you charge to 90%, or is it the other way around. It's printed on the box...
Similar Threads
-
A question about the pressure drop in coil .
By jackcn in forum FundamentalsReplies: 20Last Post: 13-12-2008, 05:10 PM -
pressure drop of pump return line ammonia
By Moeller in forum FundamentalsReplies: 5Last Post: 04-09-2007, 05:21 AM -
Optimal pressure drop in condensers and evaporators
By MrReds in forum RefrigerantsReplies: 8Last Post: 06-10-2006, 10:12 PM -
pressure drop of two phase flow in valves
By Hansss in forum FundamentalsReplies: 2Last Post: 24-06-2006, 05:10 PM -
TEV capacity related to pressure drop
By DaBit in forum CPU OverclockersReplies: 8Last Post: 06-12-2002, 05:11 PM