    TXV sizing with a larger condensing unit



    A customer is having issues with the noise level of a recipricating condensing unit currently installed in a self contained, self select merchandiser. Remoting the unit is not an option and the unit runs with normal sound levels for this model. He has decided to have me replace the recip with a scroll when I prented the idea as a possible solution. The present components are; condensing unit is R-22 rated a 7,200 btu with a 1/2-C TXV. The smallest scroll available to me is rated at 10,500 btu with refrigerant 134A. The question: Would I stay with the same size TXV just changing the refrigerant type? Or must I up-size the TXV to more closly match the larger Condensing unit? The evaporator coil and fan set-up will remain unchanged. Thanks , Ken



  2. #2
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: TXV sizing with a larger condensing unit

    You'd have to change the txv going from r22 to r134a anyway.
    but the txv size will remain the same, as they're rated by evap cooling capacity. You'll just have an oversized condenser, which may cause problems over condensing in cooler weather. I'd fit a fan controller on it to keep hp and lp up.
    Last edited by paul_h; 19-08-2007 at 04:33 PM.

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: TXV sizing with a larger condensing unit

    The bigger issue is the capaicity of the new scroll compressor. It's capacity on R-134a is already 30% greater than the smaller R-22 compressor. That will cause the system to operate with much lower suction pressures too.
    If all else fails, ask for help.


  4. #4
    Join Date
    Oct 2006
    Location
    CORDOBA -ARGENTINA
    Age
    75
    Posts
    69
    Rep Power
    18

    Re: TXV sizing with a larger condensing unit

    You need to change the condenser coil too , as the scroll y bigger.
    There is on matter on how big the condenser is , because the TXV will open or close as needed , and the flow will as much the TVX allow.
    But you will need to match the condenser coil and fan with the new compressor.

  5. #5
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: TXV sizing with a larger condensing unit

    Ken, the quietest compressors are the hermetic reciprocating compressors. Do you have a semi-hermetic? If so, just change it to a hermetic. A scroll will not be quieter than a hermetic.

  6. #6
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: TXV sizing with a larger condensing unit

    Hi there,

    I would worry about the oil first.
    R22 uses mineral oil but R134a uses synthetic one. Washing the old oil out is the major concern here. If your equipment is changed properly but the contaminated oil is there then the system would not work.
    Be very careful.

    Cheers
    Even Einstein Asked Questions

  7. #7
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: TXV sizing with a larger condensing unit

    As Lana points out you'd need to use an R12 drop in with the R134a compressor for oil compatability not to be a problem.

    Jon

  8. #8
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: TXV sizing with a larger condensing unit

    Another issue is the orifice and the distributor fro the R-134a vs the one on the coil fro R-22.

    I don't feel you will get any appreciable reduction in noise on the condensing unit with a different compressor.

    The noise you are getting...is it coming from the compressor itself, the mounting structure of the fan? Have you tried a better mount for the unit with vibration absorbers under the frame?

    I have a small scroll on my home A/C as I did on the last house. It sounds like a trash can full of rocks when it starts and then quietens down after the initial rattling.

    Ken
    Last edited by TXiceman; 21-08-2007 at 04:58 PM.

  9. #9
    Join Date
    Dec 2005
    Location
    USA
    Posts
    222
    Rep Power
    20

    Re: TXV sizing with a larger condensing unit

    Thanks to all for your suggestions and advice and it is now done! The entire condensing unit was changed to 134A and as suggested I used a 1/2 c TXV. As far as the oil goes there was no burnout so I blew the evap coil with dry nitrogen and there wasn't much oil in it. Changed the TXV and installed the cond unit. Set lpc to cycle for the 134a @ CI 34psi and CO @14psi and after adjusting the superheat the box temps are at about 36*f which is great! I wasn't really sure what the noise levels were going to be but this customer was willing to take the risk and boy did it pay off. It is nearrly silent!. The only complaint now is the evaporator and condenser fans being louder than the compressor. This was one project that came out better than I expected.
    The noise you are getting...is it coming from the Compressor itself, the mounting structure of the fan? Have you tried a better mount for the unit with vibration absorbers under the frame?
    [/QUOTE]actualy it was the valve sound all recips make. There wasn't anything wrong all normal. This customer is just a bit picky and willing to pay for what he wants.

    Thanks again, Ken
    Last edited by kengineering; 22-08-2007 at 12:53 AM. Reason: to answer a post

  10. #10
    Join Date
    Jul 2007
    Location
    united states
    Age
    43
    Posts
    21
    Rep Power
    0

    Re: TXV sizing with a larger condensing unit

    Quote Originally Posted by Dan View Post
    Ken, the quietest compressors are the hermetic reciprocating compressors. Do you have a semi-hermetic? If so, just change it to a hermetic. A scroll will not be quieter than a hermetic.

    Damn! I have read several posts before I got to this one. Good going Dan, right on target. Changing a recip to scroll has got to be going in the wrong direction. Stop the MADNESS!

  11. #11
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: TXV sizing with a larger condensing unit


    Damn! I have read several posts before I got to this one. Good going Dan, right on target. Changing a recip to scroll has got to be going in the wrong direction. Stop the MADNESS!
    Thanks, CK, but I guess Ken got it all better with a scroll, judging by his last post. But there is a lot to be said about a compressor welded housing with a compressor mounted on springs inside it to keep things quiet. I do not find scroll compressors all that quiet.

  12. #12
    Join Date
    Dec 2005
    Location
    USA
    Posts
    222
    Rep Power
    20

    Re: TXV sizing with a larger condensing unit

    Changing a recip to scroll has got to be going in the wrong direction. Stop the MADNESS!
    I was not aware the scrolls would be considered more noisy than a hermetic recip. I haven't any experience with them but many of our customers are asking for them so I'd better learn fast. I beleive it's the sales people. Any buzz-word to stimulate sales. But I must say I had done eveything possible to the Hermetic before changing it out for the scroll and the results amazed me. I cannot hear the new compressor at all. Even after defrost when presures are up you can't hear it. The chat seems to be anti-scroll? Or am I just reading into it? Please tell me what you guys really think about them. As I said, there's a buzz about scrolls in Kengineering land. Thanks, Ken
    Last edited by kengineering; 25-08-2007 at 11:50 PM. Reason: spelling

  13. #13
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: TXV sizing with a larger condensing unit

    Quote Originally Posted by kengineering View Post
    I was not aware the scrolls would be considered more noisy than a hermetic recip. I haven't any experience with them but many of our customers are asking for them so I'd better learn fast. I beleive it's the sales people. Any buzz-word to stimulate sales. But I must say I had done eveything possible to the Hermetic before changing it out for the scroll and the results amazed me. I cannot hear the new compressor at all. Even after defrost when presures are up you can't hear it. The chat seems to be anti-scroll? Or am I just reading into it? Please tell me what you guys really think about them. As I said, there's a buzz about scrolls in Kengineering land. Thanks, Ken
    Ken, I was wondering if you had a semi-hermetic reciprocating compressor and if so, suggested a hermetic. My experience with scrolls is that they are touted as the quietest compressors, but I have found them to be noisy often. If you are saying that you went from a hermetic reciprocating compressor to a scroll and it became much quieter, I stand corrected. My experience with scrolls are mostly the larger sizes.

  14. #14
    Join Date
    Dec 2005
    Location
    USA
    Posts
    222
    Rep Power
    20

    Re: TXV sizing with a larger condensing unit

    Quieter without a doubt but small yes it was a 12,500 btu copeland. The smallest they make I believe. Ken

Similar Threads

  1. ACC condensing unit 50/60 HZ
    By jan willem in forum Trouble Shooting
    Replies: 7
    Last Post: 07-06-2007, 09:37 PM
  2. M I T S U S H I T A ac unit with no condensing unit
    By Chinua in forum Air Conditioning
    Replies: 2
    Last Post: 28-07-2006, 06:54 PM
  3. York/Bristol Condensing Unit
    By Abe in forum Commercial
    Replies: 1
    Last Post: 03-02-2003, 07:46 PM
  4. Matching Evaporator with Condensing Unit
    By Abe in forum Technical Discussions
    Replies: 12
    Last Post: 25-07-2001, 08:57 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •