    Split System max pipe run length?



    Hi,
    Anyone know off the top of their head what might be the recommended pipe run length for a 12,000Btu Split. The unit is under performing, 2 years old, little use, it's in a first floor bedroom, Outdoor unit at ground level, and pipe run of approx 15metres. My view is that it is about double the recommended maximum. What do you think ?



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Split System max pipe run length?

    Need to know the make and model really but as a guess 10m max separation and 5m lift/drop.

  3. #3
    Join Date
    Jun 2007
    Location
    South Africa
    Age
    66
    Posts
    120
    Rep Power
    17

    Re: Split System max pipe run length?

    On average, a 12000 Btu unit has a maximum pipe run of about 7 meter on most makes.

    Remember that nowadays the capillary tube sits in the outdoor unit. That means that your long pipe run with the small diameter pipe is now part of the evaporator, which actually means that you are sitting now with a oversize evaporator!

    How are the 2 pipes insulated? Seperately or both in one insulation or no insulation?

  4. #4
    Join Date
    Jun 2007
    Location
    Cyprus
    Age
    73
    Posts
    252
    Rep Power
    17

    Re: Split System max pipe run length?

    Pipes are insulated seperately. 2.5M outside, then buried into the concrete wall, vertical 4M, Then across bedroom floor 6M and up inside wall again another 2.5M to indoor connection. Therefore total vertical 6.5M ... As you say even on quarter tube, this is a lot of extra evaporator and a lot of strain on the system... Thanks.

  5. #5
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Split System max pipe run length?

    Quote Originally Posted by fridge doctor View Post
    Hi,
    Anyone know off the top of their head what might be the recommended pipe run length for a 12,000Btu Split. The unit is under performing, 2 years old, little use, it's in a first floor bedroom, Outdoor unit at ground level, and pipe run of approx 15metres. My view is that it is about double the recommended maximum. What do you think ?
    It varys between make and model, but normally they are precharged for 7m. Some have a max of 10m, some have a max of 15m. At the bare minimum it would need extra refrigerant. But getting the make and model and finding someone with the installation data would be the best bet.

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. System Burn Out Troubleshooting
    By altaf22m in forum Technical Discussions
    Replies: 13
    Last Post: 07-05-2010, 09:24 AM
  3. coil temp for r22 split system
    By ctct in forum Air Conditioning
    Replies: 3
    Last Post: 28-07-2007, 09:36 PM
  4. extra length v pipe size v additional charge
    By misterfixit in forum Air Conditioning
    Replies: 18
    Last Post: 03-01-2007, 07:57 PM
  5. Split type wall mounting Air Conditioning system
    By stevews in forum Air Conditioning
    Replies: 23
    Last Post: 11-07-2005, 09:55 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •