    Question the carrier split draw amper more than notmal



    Hi My Friend.

    we have 27 carrier split unit (type 38QG18H) in our plant. the normal amper of the outdoor units are 8.6 amp but all of them draw approximately 10.5 amp .
    they are working about 3 years, if it is possible damaged the compressors.



  2. #2
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: the carrier split draw amper more than notmal

    What are the pressures like though?
    Is it drawing more current because the head pressure is high (high ambient, dirty condenser etc)?
    Are they running on heat or cool?
    Is the mains power in spec (right voltage/frequency)
    Have they been tested previously and found OK, and only increased recently? Or is this just the first time in 3 years any one has checked them?

  3. #3
    Join Date
    Jun 2007
    Location
    IRAN - ASSALUYEH
    Age
    47
    Posts
    23
    Rep Power
    0

    Re: the carrier split draw amper more than notmal

    my friend.
    why the compressore do not burn out?

  4. #4
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: the carrier split draw amper more than notmal

    It's normal to draw more than it's rated amps on a split system in certain conditions. Things I mentioned cause them to draw more amps.
    The amps it's exceeding is the outdoor unit rated amps, (as given by the manufacturer of the split), not the compressors own rated amps.

  5. #5
    Join Date
    Jul 2007
    Location
    Malta
    Age
    43
    Posts
    8
    Rep Power
    0

    Re: the carrier split draw amper more than notmal

    I think you shoud check first the gas.If there is no proper gas the compressor can get over heating and more amps.Give us more details like R 22 .......i can't find the specification for this unit.Pls be more detail that we can help you out fast and proper .Thx

  6. #6
    Join Date
    Nov 2006
    Location
    Australia
    Age
    59
    Posts
    14
    Rep Power
    0

    Re: the carrier split draw amper more than notmal

    hello karimihassan,
    you say all 27 units are drawing high amperage. you have a much higher outdoor ambient temperarture in iran than what the units are rated at, generally the units are rated at a 35 degrees celsius. in iran you would have a much higher ambient temperature than this. you say there are 27 units, when these are operating at the same time there may be a lower voltage supply. you can check if the power supply to the system is 240 volts, if the supply voltage is lower then a higher amperage reading can be expected. the compressors should have a thermal overload to protect from motor winding burn out. check that the suction line is sweating back or at least coming back cold to the compressor, i dont know if a suction line would sweat in your part of the world where humidity can be very low. also check the sun is not shining directly onto the outdoor unit coil. check that the indoor unit is giving more than 10 k (degrees) temperature difference between air on and air off the fan coil unit and that the filters are clean.
    Last edited by penair; 19-08-2007 at 12:25 AM.

Similar Threads

  1. York / Carrier/ Whirlpool ..split A/c
    By fireblade in forum Air Conditioning
    Replies: 2
    Last Post: 24-07-2006, 12:03 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •