    fault on a sanyo unit



    Hi guys, just got a call from a guy at work, who is on call tonight. He got called to a restaurant with 4 indoor sanyo cassettes and one multi out door. The problem is the controller is flashing E04 ( comms error?) problem is im trying to guide him through what to do from here. Iv told him to check the basics i.e power to the outdoor, voltage of the outdoor PCB any blown fuses etc. Are there any sanyo experts around to help as the technical number for sanyo is closed until monday



  2. #2
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    985
    Rep Power
    19

    Re: fault on a sanyo unit

    Paul


    "KEEP IT COOL"

  3. #3
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,876
    Rep Power
    28

    Re: fault on a sanyo unit

    Quote Originally Posted by techguy View Post

    Power to the outdoor PCB
    The 0.6Ma fuse on both PCBs its soldered on
    If this fuse is gone
    Check the control Cable
    If this is OK then There is a brown plug on both indoor and outdoor PCB's marked EMG.
    This is on the off side of the fuse Make sure all cables are OK as if there is anything wrong with comms cabling this can blow the PCB if this plug is used.

    Providing comms cables are OK

    Change the blue comms plug with the pink and blue wires into this EMG socket on Both indoor and outdoor PCB's

    If this doesn't work this snip v006 off the outdoor PCB and try again
    Would it be the same on a mutli unit?

  4. #4
    Join Date
    Dec 2004
    Location
    manchester
    Posts
    97
    Rep Power
    20

    Re: fault on a sanyo unit

    speak to someone at ICG in stockport who supply us with sanyo kit, we have found them always willing to help.

    ICG-01614294800

  5. #5
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,876
    Rep Power
    28

    Re: fault on a sanyo unit

    thanks Dannycool, but i already have that number and i tried to ring them the other day but they were closed until monday.

  6. #6
    Join Date
    Dec 2004
    Location
    manchester
    Posts
    97
    Rep Power
    20

    Re: fault on a sanyo unit

    oh right, well if you pm me your email add, i can send you a pdf of the sanyo service manual, if thats of any use.

  7. #7
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    70
    Posts
    604
    Rep Power
    18

    Re: fault on a sanyo unit

    Hi Marc,
    Do you know what system this is ....SAP or SPW?

    Guess as you talk about a controller, it is a wired controller so that it will probably be a SPW system (SAP have Infra Red controls). Any chance of a model # ?
    E04 is generally Indoor unit is detecting an error signalled from the outdoor unit: Error in receiving serial communications signal.

  8. #8
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,876
    Rep Power
    28

    Re: fault on a sanyo unit

    Quote Originally Posted by Electrocoolman View Post
    Hi Marc,
    Do you know what system this is ....SAP or SPW?

    Guess as you talk about a controller, it is a wired controller so that it will probably be a SPW system (SAP have Infra Red controls). Any chance of a model # ?
    E04 is generally Indoor unit is detecting an error signalled from the outdoor unit: Error in receiving serial communications signal.
    I dont know what model it is until the guy rings me back and lets me know, if it hasnt been sorted already then i expect il be called to it on monday morning.

Similar Threads

  1. Fault on an Airedale unit
    By marc5180 in forum Air Conditioning
    Replies: 50
    Last Post: 30-06-2007, 06:10 PM
  2. Sanyo fault
    By casstle in forum Air Conditioning
    Replies: 1
    Last Post: 20-06-2007, 11:22 PM
  3. Sanyo CR 903GY Multi Unit
    By bobjob in forum Air Conditioning
    Replies: 0
    Last Post: 29-07-2006, 04:27 PM
  4. Sanyo inverter split unit
    By cikku in forum Domestic
    Replies: 3
    Last Post: 22-05-2006, 06:07 PM
  5. MHI, Sanyo & Fuijitsu Complete Fault Codes
    By aeb200 in forum Air Conditioning
    Replies: 1
    Last Post: 16-11-2005, 02:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •