    3 phase compressor



    i have a rooftop 10 ton 3 phase unit (2- 5 ton hermetic compressors) and had one of the compressors go bad. I replaced the compressor with a one i took out of a unit earlier this year that i replaced. My question: Does it matter if it runs a different direction that it was in the other one?

    Thanks



  2. #2
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: 3 phase compressor

    if it runs in the wrong direction chances are you hooked the phases up wrong

  3. #3
    Join Date
    Aug 2007
    Location
    Henryville, IN
    Age
    71
    Posts
    5
    Rep Power
    0

    Red face Re: 3 phase compressor

    If it is a scroll it matters. Hook your guages up and observe. Usually the sound will tell you if you hooked it up wrong.

  4. #4
    stegmo2's Avatar
    stegmo2 Guest

    Re: 3 phase compressor

    it is a recip. I have high head low suction and was wondering if it mattered which way it runs. like i said earlier i took it out of a unit i replaced. it ran who knows what direction in the old one. i am going to replace the unit soon so i was just trying to buy time with using this other compressor.

  5. #5
    Join Date
    Jun 2007
    Location
    Cyprus
    Age
    73
    Posts
    252
    Rep Power
    17

    Re: 3 phase compressor

    It doesn't matter for a recip, hermetic or semi-hermetic. Any way is OK. Regards

  6. #6
    Join Date
    Dec 2006
    Location
    Australia
    Posts
    16
    Rep Power
    0

    Re: 3 phase compressor

    Sounds like the customer should bite the bullet and
    replace the Air Conditioner!

  7. #7
    Join Date
    Jul 2007
    Location
    Malta
    Age
    43
    Posts
    8
    Rep Power
    0

    Re: 3 phase compressor

    the best way for you is if you have a phase rotation meter to check on the old unit.

  8. #8
    Join Date
    Jun 2007
    Location
    South Africa
    Age
    66
    Posts
    120
    Rep Power
    17

    Re: 3 phase compressor

    Like fridge doctor said, if it is a piston job, it does not matter in what direction it runs. However, if it is a semi hermetic compressor with a positive displacement oil pump, it is a different scenario.

    If a semi hermetic compressor with an oil pump has worked for a amount of time in a certain direction, and you reverse the rotation, you can find that the nett oil pressure of the oil pump is lower than the previous installation or run, because!

    The oil pump tends to wear in one direction, with good oil pumping. When you change the direction, the pump must try to match surfaces in the opposite direction which could lead to insufficient oil pressure, or even sometimes (which is very rare) oil pump failure.

    When you changed the compressor, did you vacuum the whole plant or just the compressor? Why did the previous compressor go bad?

  9. #9
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: 3 phase compressor

    How do you know which way the compressor is running?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  10. #10
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: 3 phase compressor

    Quote Originally Posted by Brian_UK View Post
    How do you know which way the compressor is running?
    LOL... thats what I was wondering.

    Did you strip the end plate off and then switch it on?

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  11. #11
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: 3 phase compressor

    Or if a hermetic maybe he fitted a sight glass in the shell
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  12. #12
    stegmo2's Avatar
    stegmo2 Guest

    Re: 3 phase compressor

    Thanks fridgedoc and eeram! Im glad we have people with real answers instead of moderators trying to be comedians. The old one was 25 years old and had an open winding. I cleaned it all and installed the used compressor it seems to be working now. I had worked on the 06L carriers and as you said it matters with a positve displacement oil pump. I didn't know about the others. Hopefully won't have to rig anymore.
    thanks again

  13. #13
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: 3 phase compressor

    Just trying to lighten the place up a little...lol
    hermetic compressors
    Now you say its a recip?

    A little more info on the 1st post would have helped.

    If the direction worries you just swap any two phase connections round and it will spin the other way.

    Chillin
    Last edited by chillin out; 19-08-2007 at 08:59 PM. Reason: Missunderstood.
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  14. #14
    Join Date
    Nov 2006
    Location
    Australia
    Age
    59
    Posts
    14
    Rep Power
    0

    Re: 3 phase compressor

    you guys really go off the channel sometimes, (end plate?). stegmo said the compressor is hermetic..... if he is getting low pressure suction and high pressure discharge on the gauges then all is well.....
    Last edited by penair; 19-08-2007 at 12:48 AM. Reason: spelling

  15. #15
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: 3 phase compressor

    Quote Originally Posted by penair View Post
    you guys really go off the channel sometimes, (end plate?). stegmo said the compressor is hermetic..... if he is getting low pressure suction and high pressure discharge on the gauges then all is well.....
    Please re-read the thread properly.

    He started off saying it was a hermetic then changed it.

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  16. #16
    Join Date
    May 2007
    Location
    NC
    Posts
    262
    Rep Power
    17

  17. #17
    Join Date
    Sep 2007
    Location
    Casa Grande, Arizona
    Age
    61
    Posts
    19
    Rep Power
    0

    Re: 3 phase compressor

    When a compressor starts up wont its movement from the torque of starting indicate the direction its turning? Never thought of "compressor direction" until I read this post, ya learn something new all the time!

Similar Threads

  1. Three Phase Compressor
    By joeslad in forum Trouble Shooting
    Replies: 33
    Last Post: 04-12-2009, 07:00 PM
  2. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  3. Replies: 5
    Last Post: 09-08-2007, 01:29 AM
  4. Three Phase Compressor
    By joeslad in forum Trouble Shooting
    Replies: 1
    Last Post: 12-10-2005, 11:37 PM
  5. Compressor pumping efficiency
    By shogun7 in forum Fundamentals
    Replies: 0
    Last Post: 25-02-2004, 10:50 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •