Results 1 to 8 of 8
Thread: Black Oil
    Jan 2007
    MEXICO
    Black Oil
    Why the lubricant loss viscosity and get black color when i work with hydrocarbons like refrigerants?
    Thanks in advance
    Mar 2005
    71
    639
    14
    Re: Black Oil
    The viscosity loss is due to the saturation of the oil with the HC you are running. You have to use an oil that does not readily absorb the HC.
    The black color is most likely a contaminate from either the HC or a problem with the additive package in the oil.
    As I ahve suggest before, you need to contact CPI Engineering in Michigan, http://www.cpieng.com/
    If you give then the HC composition, type compressor and operating conditions, they can generally get you into the right oil.
    Ken
    Aug 2005
    5,327
    Re: Black Oil
    The hydrocarbon refrigerants are notorious for causing oil dilution. This is one area of refrigeration you do NOT want to guess at!
    Doing so can wreck compressors very quickly.
    Oct 2003
    56
    5,519
    28
    Re: Black Oil
    Mebluna, system started up without proper evacuation.
    Mar 2005
    71
    639
    14
    Re: Black Oil
    You need a complete gas analysis. I have need some trace gases in the HC give the oil a really bad time. In particular, SO2 and H2S along with a little water vapor.
    Is this closed loop or an open loop system?
    Ken
    Jan 2007
    MEXICO
    Re: Black Oil
    I´have Analized The Gas, I Don´t Have So2, H2s.
    And I Can´t Change The Oil Because It Is A Trane System With A Scroll Compresor.
    Aug 2003
    Netherlands
    43
    621
    15
    Re: Black Oil
    What kind of Trane unit do you have?
    Most of the Trane scroll's have a tap in the side. Except for the first scroll compressors all have a tap with either a valve, schräder or plug in it.
    Nov 2006
    Australia
    14
    Re: Black Oil
    i think peter1 said it best, you have moisture in the system.
  1. convection/adsorption wind tunnel
    By duke in forum New Technologies
    Last Post: 09-07-2007, 09:16 PM
  2. Brown or Black plastic box trunking
    By alex242 in forum Air Conditioning
    Last Post: 07-05-2007, 10:06 AM
  3. Energy saving black boxes
    By Rackman in forum Supermarket Refrigeration
    Last Post: 26-06-2006, 05:12 AM
  4. Black Fell Terrier
    By subzero*psia in forum Hobbies
    Last Post: 25-10-2001, 01:55 AM
