    problems with york yaa c chiller



    hi can anyone help please been out to a york chiller it has 4 scroll comps working as 2 circuits 1and 2 useing common discharge and suction on each circuit, the prob is the unit is only useing a max of 2 comps at any time even if its not acheived temp the control display does not even show any run hours for comps 2 and 3 but in the service mode the system shows the all comps with 0 run time on 2 comps the unit has its eprom changed but no change would be gratefull of any input cheers guys



  2. #2
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,471
    Rep Power
    41

    Re: problems with york yaa c chiller

    paul

    you need the service password, check that the model is correct in the program and that the correct number of compressors is programmed. i havn't worked on one in ages so i can't remember the password and i could also be completely off the mark!!

    al

  3. #3
    Join Date
    Aug 2007
    Location
    ENGLAND
    Posts
    63
    Rep Power
    17

    Re: problems with york yaa c chiller

    hi al have checked all that mate all seems ok thanks for your reply

  4. #4
    Join Date
    Feb 2007
    Location
    England
    Age
    49
    Posts
    15
    Rep Power
    0

    Re: problems with york yaa c chiller

    hi, l haven't worked on one of these for a while so it's a bit sketchy, l know this sounds stupid but are both circuits turned in in the options key?? you said it's had a new eprom if so you may need to re program the chiller and this may be why it says o run hours. l think you press program and then it's a combo of up and down keys pos up up down down up up. try a few examples until you get in oh and press enter. let me know if this helps. neil.

  5. #5
    DjP67's Avatar
    DjP67 Guest

    Re: problems with york yaa c chiller

    What is the age of the chiller ?
    Has the board got toggle switches for the compressors ?
    are they switched on ?
    Is the loading sequence correct (as in can it see the other compressos) ?

Similar Threads

  1. York Chiller
    By HVACGod in forum Commercial
    Replies: 12
    Last Post: 11-09-2010, 06:05 AM
  2. York Chiller
    By RubenJLL in forum Trouble Shooting
    Replies: 20
    Last Post: 18-04-2008, 04:08 PM
  3. York Screw Chiller How low will it go?????
    By bruceboldy in forum Industrial Compressors
    Replies: 11
    Last Post: 10-08-2007, 10:29 PM
  4. york chiller help please
    By airconadam in forum Air Conditioning
    Replies: 15
    Last Post: 21-04-2007, 01:31 PM
  5. York process chiller repairs
    By Matt in forum Commercial
    Replies: 5
    Last Post: 24-03-2004, 12:07 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •