Thread: problems with york yaa c chiller
-
15-08-2007, 08:50 PM #1
problems with york yaa c chiller
hi can anyone help please been out to a york chiller it has 4 scroll comps working as 2 circuits 1and 2 useing common discharge and suction on each circuit, the prob is the unit is only useing a max of 2 comps at any time even if its not acheived temp the control display does not even show any run hours for comps 2 and 3 but in the service mode the system shows the all comps with 0 run time on 2 comps the unit has its eprom changed but no change would be gratefull of any input cheers guys
-
15-08-2007, 09:17 PM #2
Re: problems with york yaa c chiller
paul
you need the service password, check that the model is correct in the program and that the correct number of compressors is programmed. i havn't worked on one in ages so i can't remember the password and i could also be completely off the mark!!
al
-
15-08-2007, 09:20 PM #3
Re: problems with york yaa c chiller
hi al have checked all that mate all seems ok thanks for your reply
-
18-08-2007, 07:24 PM #4
Re: problems with york yaa c chiller
hi, l haven't worked on one of these for a while so it's a bit sketchy, l know this sounds stupid but are both circuits turned in in the options key?? you said it's had a new eprom if so you may need to re program the chiller and this may be why it says o run hours. l think you press program and then it's a combo of up and down keys pos up up down down up up. try a few examples until you get in oh and press enter. let me know if this helps. neil.
-
21-08-2007, 08:20 PM #5
Re: problems with york yaa c chiller
What is the age of the chiller ?
Has the board got toggle switches for the compressors ?
are they switched on ?
Is the loading sequence correct (as in can it see the other compressos) ?
Similar Threads
-
York Chiller
By HVACGod in forum CommercialReplies: 12Last Post: 11-09-2010, 06:05 AM -
York Chiller
By RubenJLL in forum Trouble ShootingReplies: 20Last Post: 18-04-2008, 04:08 PM -
York Screw Chiller How low will it go?????
By bruceboldy in forum Industrial CompressorsReplies: 11Last Post: 10-08-2007, 10:29 PM -
york chiller help please
By airconadam in forum Air ConditioningReplies: 15Last Post: 21-04-2007, 01:31 PM -
York process chiller repairs
By Matt in forum CommercialReplies: 5Last Post: 23-03-2004, 11:07 PM