    alarm cancelation problem



    Hello everyone I am new and I am asking for help.
    I have 1997 GEA Grasso ammonia screw compressor and I can not cancel the high pressure discharge alarm.Every time I try, the screen says "alarm canceled" but the alarm comes back again and again.



  2. #2
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: alarm cancelation problem

    Did you reset the high pressure pressostat?

  3. #3
    kazik1996's Avatar
    kazik1996 Guest

    Re: alarm cancelation problem

    I do not now haw to do it.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: alarm cancelation problem

    Quote Originally Posted by kazik1996 View Post
    I do not know how to do it.
    Worrying
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: alarm cancelation problem

    If it's danfoss, screw the top of and reset is under the cover.

    If it's any other brand, there should be a reset button somewhere under the cover, if not it's auto reset and either the pressure is still to high or the pressostat is broken!

Similar Threads

  1. Dunham Bush Chiller Alarm
    By Regulator in forum Air Conditioning
    Replies: 11
    Last Post: 08-12-2010, 01:42 AM
  2. A strange problem
    By MuhengineeR in forum Air Conditioning
    Replies: 14
    Last Post: 27-10-2010, 05:21 PM
  3. voltage drop on relay
    By Temprite in forum Electrical
    Replies: 4
    Last Post: 30-01-2006, 07:55 PM
  4. Condensation Problem At Door to Freezers
    By mmarch in forum Air Conditioning
    Replies: 5
    Last Post: 17-10-2005, 02:42 PM
  5. LG 10.5 kw cassette timer problem
    By Andy W in forum Air Conditioning
    Replies: 10
    Last Post: 25-06-2005, 07:09 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •