    Hi Everybody & thank you Jon

    The following is the extract from the DuPont site with regard to the R 507.

    “DuPont R-507 will maintain a very consistent composition if leakage occurs in a refrigeration system, which means that operating performance, will remain consistent following leakage/recharge cycles. As with all mixtures, we recommend that the liquid phase be removed from the storage cylinder to minimize composition changes when charging. DuPont R-507 should not be mixed with any other refrigerant when charging, recycling, recovering or reclaiming”.

    I have practical experience on a leaking R 404a system. After detecting the leak and repairing it, I could not get the original performance after topping up with R 404a. The room temperature went up by 20 deg C. As this was my first R 404a system and on the instructions from the compressor manufacturer I fully evacuated the balance refrigerant and charged with fresh R 404a liquid, and immediately the performance came back to normal and working at Te -35 deg C.

    As such I want to change all my equipments to R507. Please let me know about you practical experience on R507.

    Suny



  2. #2
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: About R 507

    r404a = r507 with r134a added. ie r404a is more a zeotrpoic blend than r507. The two base compounds are the same for each of them, but for some unknown reason r404a has r134a added.
    I do a lot of work on commercial kitchens with 3-4kg charges, and only bother carrying r507 in my van. I've never had a problem on such small systems topping up with r507.

  3. #3
    Join Date
    Dec 2006
    Location
    Philippines
    Age
    44
    Posts
    16
    Rep Power
    0

    Re: About R 507

    I have replaced all equipment under our Preventive Maintenance which have the r404 charge with the 507 refrigerant as i have noticed that the r404 is very prone to leakage and is not advisable to add up when theres a leakage on the system.

  4. #4
    Join Date
    Jun 2007
    Location
    Sri Lanka
    Posts
    88
    Rep Power
    0

    Re: About R 507

    Paul H & Philip

    Thank you for your comments. I am going to replace R 404a with R 507. The mfg’s agent advised me to use the same TEV for R 507. Any comments on this will be appreciated.

    Suny

  5. #5
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: About R 507

    Hi Suny,
    Yes the TEV is good for both R404a and R507. I always use 507 where possible.

  6. #6
    Join Date
    Jun 2007
    Location
    Sri Lanka
    Posts
    88
    Rep Power
    0

    Re: About R 507

    Thank you Electrocoolman. The system is working perfectly.