Results 1 to 13 of 13
13-08-2007, 11:18 PM #1
Daikin Error Code AH, Sky Air + VAM HRV
I've got a site with three individual Sky Air systems and what I thought was a separate VAM2000 HRV unit.
All these are switched via the main HVAC panel with fault reporting.
One of the remote controllers will sometimes go into error mode with an AH fault code relating to the VAM unit. As far as I know AH stands for an extremely dirty filter.
This might be fair enough but I can't see how the fault code is getting sent to the split when there is only a two wire connection to the control panel as far as I can make out.
Frank - H E L P
14-08-2007, 12:26 AM #2
Re: Daikin Error Code AH, Sky Air + VAM HRV
Hi Brian, is the sky air unit and the VAM unit controlled off the one remote controller? Also can you advise exact model numbers of both sky air unit and Vam unit?
20-08-2007, 06:10 PM #3
The controll and fault display on the Daikin unit is very advanced and would be able to send the information you refer to to the controller. There could be a set up issue if this info is not required on that particular controller.
20-08-2007, 07:14 PM #4
AH Malfunction of air filter maintenance
see atached
an old fault maybe? have you cleared the fault memory?Paul
"KEEP IT COOL"
20-08-2007, 07:54 PM #5
Hi Brian
It's not a code that I've come across (possibly because I always clean my filters )
I've spoken to Daikin who acknowledge the fault code but tell me that there is no flow chart available for this code ??
They say that it can sometimes be a spurious code and should be able to clear (keep your finger on the on/off button for 10 secs with the fault code showing).
Failing that I can't really help
20-08-2007, 08:05 PM #6
Thanks Frank, yes the filters are cleaned very regularly and by me so I can't push any complaints on that side.
I am intrigued that the remote knows about the VAM when I can't see any electrical connection. Note to self, have a better look up in that ceiling.
I'll keep an eye on this, thanks again.Brian - Newton Abbot, Devon, UK
20-08-2007, 08:47 PM #7
20-08-2007, 09:04 PM #8
Yep, vacuumed with a soft brush head.
Will have a better look at the wiring next time.
By the way - why do ceiling grids always conflict with anything that has been fitted above it?
Is it a Dilbert thing?Brian - Newton Abbot, Devon, UK
05-04-2008, 02:44 PM #9
Hello everyone,
I am new to this forum and have found it very imformative.
I had a Daikin FDYQ160M ducted unit installed and working, but showing E9 error code. Can you Paul or Frank tell me how to clear the fault memory.
Thanks in advance.
Vann.
05-04-2008, 04:41 PM #10
eev faulty
06-04-2008, 12:08 AM #11
08-04-2008, 01:50 PM #12
If you have fixed the fault then to clear the last fault code display you need to press the lower left hand button once (to bring the fault code up) then press and hold the on/off button for 5 seconds until the fault code disappears
This doesn't clear the fault history log of the last 10 fault codes
Obviously, if you haven't fixed the fault then you cannot clear the fault code
11-04-2008, 11:50 PM #13
Thanks Frank, Brian and 1torr,
Regards,
Vlao
Daikin not working... many problems
By stankovicv in forum Air ConditioningReplies: 26Last Post: 11-12-2010, 09:01 AM -
Daikin, Why do we bother?
By gwilliamson in forum Air ConditioningReplies: 21Last Post: 02-02-2010, 09:38 AM -
Daikin Controllers
By airefresco in forum Air ConditioningReplies: 5Last Post: 15-05-2008, 08:08 AM -
!!big Daikin Problem!! Codes,u4,pj, And E0
By airconengineer in forum Air ConditioningReplies: 21Last Post: 31-05-2007, 09:04 PM -
DAIKIN - Weybridge: How to get a Quote.
By Makeit go Right in forum Air ConditioningReplies: 12Last Post: 25-04-2007, 08:50 PM