    High Side Pressure is ...

    I got this service call the other day. It was a 2ton keeprite ultraquiet residential a/c system. The complaint was that the A/C doesnt shut off and runs continiously. On my inspection the pressure were a litttle low, and condenser unit was very dirty. So i topped up the refrigerant and cleaned the condenser coil.
    The pressure on low side was 70psi and High Side 160Psi. with R22 refrigerant and temperature outside was about 88F. I dont know why the high side pressure is too low? Any idea as to why the high side pressure lines feel cold and has low pressure?

  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: High Side Pressure is ...

    Did you do a leak test before 'topping up'?

    Is the compressor pumping correctly?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: High Side Pressure is ...

    If we take a step back.....

    Did you connect your gauges to the service ports on the outside side of the outdoor unit?
    Were both pipes lagged?(sorry never worked on these units)

    If the answer to both these questions is YES, then you measured an intermediate pressure and not a true HP.

  4. #4
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: High Side Pressure is ...

    Quote Originally Posted by SULTAN View Post
    I got this service call the other day. It was a 2ton keeprite ultraquiet residential a/c system. The complaint was that the A/C doesnt shut off and runs continiously. On my inspection the pressure were a litttle low, and condenser unit was very dirty. So i topped up the refrigerant and cleaned the condenser coil.
    The pressure on low side was 70psi and High Side 160Psi. with R22 refrigerant and temperature outside was about 88F. I dont know why the high side pressure is too low? Any idea as to why the high side pressure lines feel cold and has low pressure?
    It sounds the system has leakage, both the low-side and high-side pressure are low. It can also deduced from the low values of the condensing and evaporating temperatures 80.71F and 30F although the condenser was fouled and the ambient temperature is above the condensing temperature. So it is better to check the leakage matter firstly?.

  5. #5
    Join Date
    Aug 2007
    Location
    NZ
    Age
    56
    Posts
    18
    Rep Power
    0

    Re: High Side Pressure is ...

    Hi, could be a leaking reversing valve, 70psi could be high depending o room temp.

  6. #6
    Join Date
    Aug 2007
    Location
    Malawi
    Age
    40
    Posts
    19
    Rep Power
    0

    Re: High Side Pressure is ...

    i would recomend that you check if the compressor pumping efficiently, and verify that there are no leaks.

Similar Threads

  1. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  2. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM
  3. High head pressure no duty
    By LRAC in forum Commercial
    Replies: 15
    Last Post: 23-07-2007, 12:12 AM
  4. Replies: 6
    Last Post: 18-11-2005, 05:30 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •