    Arrow Frick RTM120SEB8 vibration concern



    Hi Guys
    I've a strange vibration on one of my compressors, when it is running between 15% and 45-50% of capacity ,it vibrate like hell, I'm not very familiar with Frick compressors as I'd usualy worked with Stal compressors. I can definetly say that is not a problem related to liquid refrigerant coming back on the suction line as i switch the compressors with the spare unit and this ones is running fine... I'd contact York service and they siad that up to 11mm/s vibration value is fine , but I don't trust them very much as with our VSM89 chillers warranty problem ,they were more concern to cover them up instead to solve them.....
    Anybody has any suggestion or comments?
    I'm planning to open the compressor as an apple and replace the berarings and inspect the screw conditions...
    Ciao
    Evapcooil



  2. #2
    Join Date
    May 2007
    Location
    The Netherlands
    Age
    54
    Posts
    30
    Rep Power
    0

    Re: Frick RTM120SEB8 vibration concern

    Hi evapcoil,

    as far as my experience with frick compressors goes I'm certain that 11 mm/s is way too much. These compressors (when properly aligned and in good condition) can easily run between 1 and 3 mm/s. So check alignment and coupling (if it is rubber type inspect it very precise). If these are OK. Something must be wrong with the compressor.

    Regards

    The Screwdoctor

  3. #3
    Join Date
    Aug 2007
    Location
    on the sea
    Age
    48
    Posts
    75
    Rep Power
    17

    Re: Frick RTM120SEB8 vibration concern

    Thank You Doc
    I'll check the coupling, regarding the alignment, the compressor is mounted directly on the electrical motor drive end flange so I don't think this should be bad....
    Do You have any idea where i can find a service manual for this compressor???

  4. #4
    Join Date
    Mar 2006
    Location
    Norfolk
    Posts
    160
    Rep Power
    19

    Re: Frick RTM120SEB8 vibration concern

    Vibration under partial load can be a sign of bearings going.

    Get a long shafted screwdriver and when the vibration is occuring place the blade on to the compressor and the handle to your ear. By trying various places you should be able to pinpoint the vibration.


    Paula

  5. #5
    Join Date
    Aug 2007
    Location
    on the sea
    Age
    48
    Posts
    75
    Rep Power
    17

    Re: Frick RTM120SEB8 vibration concern

    Actually, I'm thinking to through a complete overhaul of the unit as the vibration are at 14mm/s and the solution that Frick?York suggest is to put some weight on the discharge pipe??????????
    I'll keep You posted....

  6. #6
    Join Date
    May 2007
    Location
    The Netherlands
    Age
    54
    Posts
    30
    Rep Power
    0

    Re: Frick RTM120SEB8 vibration concern

    That would be nice, put some weight somewhere and all your problems are solved. What kind of advise is that??? You made the right decision to strip down the compressor. Something must be wrong with bearings, rotorpair.

    The Screwdoctor

  7. #7
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Frick RTM120SEB8 vibration concern

    Sounds like you need to find a new Frick service center. They are just blowing smoke up your skirt to make you go away.

    If you are getting these vibration levels at part load, what levels are you getting at full load? Also, at what frequencies do the vibrations occur. Are they at the driven speed or are they at a harmonic? Is it at 4 times the male rotor speed?

    If you are getting a lot of vibration at 4 x the male rotor speed, this is you primary pumping frequency or rotor pass frequency and this may well be a gas induced vibration due to resonance in the discharge line or oil separator.

    If the vibration is out in the 100,000 CPM range, it is bad rolling element bearings.

    Vibration at part load can act strange when you get some excessive slide valve wear at a part load point. The slide valve can rock and eventually get to the point of contacting the rotors. In this case you can also hear the noise level has increased. Excessive slide valve wear can be caused by unsteady load controls, ie., the controls are not tuned correctly and lets the compressor constantly hunt.

    Ken
    Last edited by TXiceman; 16-08-2007 at 06:52 PM.

  8. #8
    Join Date
    Jul 2005
    Location
    France- USA
    Age
    47
    Posts
    27
    Rep Power
    0

    Re: Frick RTM120SEB8 vibration concern

    Hello,

    Is your compressor and XJF 120 from Frick, if yes, open the thrust bearing cover on the back, and look if the thrust bearings on the male or female side have been rotating on the sleeve distance.

    If yes, then complete compressor overhaul is needed.

    What application and refrigerant is it working on ?

  9. #9
    Join Date
    May 2003
    Location
    Canada
    Posts
    31
    Rep Power
    0

    Re: Frick RTM120SEB8 vibration concern

    Had a similar problem, is there lots of foam in the oil seperator as well? Is this a liquid injection cooled machine?

  10. #10
    Join Date
    Aug 2007
    Location
    on the sea
    Age
    48
    Posts
    75
    Rep Power
    17

    Re: Frick RTM120SEB8 vibration concern

    Hi guys
    sorry I was absent for a while without reading the forum, the compressor is installed in a 0°C setpoint plant using R407C refrigerant.
    No ,I don't have a lot of foam in the separator and I don't have the liquid injection.

  11. #11
    Join Date
    Jul 2006
    Location
    CN
    Age
    39
    Posts
    20
    Rep Power
    0

    Re: Frick RTM120SEB8 vibration concern

    11mm/s RMS is just the requirement of ISO 2372.

    agree with Txiceman!!!

  12. #12
    Join Date
    Jul 2009
    Location
    arkansas
    Age
    42
    Posts
    18
    Rep Power
    0

    Re: Frick RTM120SEB8 vibration concern

    What size compressor is this? TDSH? SGC? XJF? BOOSTER, HIGH STAGE?

  13. #13
    Join Date
    Jul 2009
    Location
    New zealand
    Age
    47
    Posts
    15
    Rep Power
    0

    Re: Frick RTM120SEB8 vibration concern

    don't strip, first uncouple the motor from the compressor then have a vibe test done on the motor or check it yourself.

  14. #14
    Join Date
    Jul 2009
    Location
    arkansas
    Age
    42
    Posts
    18
    Rep Power
    0

    Re: Frick RTM120SEB8 vibration concern

    if this is a 231 mm compressor they do have a very bad nosie in this slide valve range. Frick has figured out the problem and still use this compressor. all it is, is a gas hormonic in the screws them selves. I would have a vibration done in it anyway at that % slide valve.

Similar Threads

  1. Frick Premature Seal Failures
    By Steve Wright in forum Industrial Compressors
    Replies: 32
    Last Post: 11-06-2010, 02:34 PM
  2. Luiquid line vibration and liquid hammer
    By Infinity in forum Trouble Shooting
    Replies: 12
    Last Post: 09-02-2007, 10:22 PM
  3. old frick system monitor
    By rasgrant in forum NH3
    Replies: 5
    Last Post: 17-01-2007, 06:15 PM
  4. Vibration in refrigerant piping
    By US Iceman in forum Technical Discussions
    Replies: 5
    Last Post: 01-05-2006, 11:53 PM
  5. Liquid Line's Vibration
    By JERRYCOOL in forum Industrial
    Replies: 20
    Last Post: 21-03-2006, 01:49 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •