    One to watch for



    Has anyone ever seen a leak on a pipe with 20psi in it and actually sucking in?

    I had a leak on a 1/4 pipe with 20 psi flowing through it and when I sprayed it it sooked inwards!!!!

    Next time the system gets shut down.

    Chillin


    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: One to watch for

    Ahh,
    The old fashioned venturi effect jet pump........

  3. #3
    Join Date
    Mar 2004
    Location
    UK
    Posts
    624
    Rep Power
    21

    Re: One to watch for

    Hi

    Chillin never seen it before but maybe this will help explain.


    http://www.animatedsoftware.com/pumpglos/jet_pump.htm

  4. #4
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: One to watch for

    Hi Bernard,

    I guessed thats why it happened, but I have never noticed it on a fridge system before.

    Makes you think about all them leak tests you done and never found a leak...

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

Similar Threads

  1. English language & interesting phrases
    By US Iceman in forum Chit Chat & Service Stories
    Replies: 122
    Last Post: 08-09-2008, 09:03 PM
  2. Bond, James Bond --
    By Paulajayne in forum Chit Chat & Service Stories
    Replies: 27
    Last Post: 05-12-2006, 11:22 PM
  3. First look...........lasting impression
    By Abe in forum Legal-Business-Marketing
    Replies: 4
    Last Post: 12-05-2002, 09:34 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •