    Chiller Probs



    Hi i recently called to a chiller plant which had faulty alinco tev . changed tev ,drier core ,p tested and vacced properly recharged with manufactures charge of r407c. Plant running and cooling water but have got high suction pressure (70psig) at normal load (water cooling to 10c and cycling properly)
    Is the valve plates on the coplenad recip comprosser at fault? i suspect discharge leaking into crankcase? help!! the comp is of 4 head type with a unload valve on 2nd head .



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Chiller Probs

    Well,
    Check how fast/if it will pump down and stay down, that's the easiest test of the valves, saying that, a copeland semi is quite easy to strip and inspect.

    Have you checked the flowrate of the water? if this is too high then it will rise the LP.

Similar Threads

  1. Dunham Bush Chiller Alarm
    By Regulator in forum Air Conditioning
    Replies: 11
    Last Post: 08-12-2010, 01:42 AM
  2. DIY aquarium chiller
    By BarraCuda in forum Technical Discussions
    Replies: 18
    Last Post: 06-10-2010, 11:02 PM
  3. York Screw Chiller How low will it go?????
    By bruceboldy in forum Industrial Compressors
    Replies: 11
    Last Post: 10-08-2007, 10:29 PM
  4. Water Chiller
    By lana in forum Technical Speculations
    Replies: 20
    Last Post: 23-06-2007, 01:19 AM
  5. Connecting Trane Water chiller to air handling unit
    By celtictech in forum Fundamentals
    Replies: 10
    Last Post: 08-03-2007, 06:14 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •