    Frick RWB II Plus Rev D Micro



    I recently had a RWB II micro freeze on me resulting in a compressor failure, when the micro froze the safeties failed, the compressor totally unloaded and the liquid injection became inactive. The alarm circuit and safety circuits under this condition became inactive. The failure was eventually found to be caused by faulty suppressors holding the package run relay in. If anyone has experienced a similar failure and found a way to repair this fault by forcing the micro to shut down or to cut the signal from the run relay, please forward me your findings.



  2. #2
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,632
    Rep Power
    24

    Re: Frick RWB II Plus Rev D Micro

    Quote Originally Posted by Vernon View Post
    I recently had a RWB II micro freeze on me resulting in a compressor failure, when the micro froze the safeties failed, the compressor totally unloaded and the liquid injection became inactive. The alarm circuit and safety circuits under this condition became inactive. The failure was eventually found to be caused by faulty suppressors holding the package run relay in. If anyone has experienced a similar failure and found a way to repair this fault by forcing the micro to shut down or to cut the signal from the run relay, please forward me your findings.
    Hi Vernon

    all micro controls have the posibility of doing the same, it is better to back up with a HP. LP oil diff (if required) and HT mechanical switch, hard wired into the control circuit inline with the control circuit to the compressor starter.

    Kind Regards Andy D
    If you can't fix it leave it that no one else will:rolleyes:

Similar Threads

  1. Frick XJF/XJS 120 compressors
    By 404cab in forum Industrial Compressors
    Replies: 21
    Last Post: 15-11-2011, 03:57 PM
  2. Frick Premature Seal Failures
    By Steve Wright in forum Industrial Compressors
    Replies: 32
    Last Post: 11-06-2010, 02:34 PM
  3. FRICK TDSH 233 Slide Valve and guide damaged
    By 404cab in forum Industrial Compressors
    Replies: 9
    Last Post: 30-07-2008, 11:24 PM
  4. Frick Micro Control Panel Problem
    By derfriguy in forum New to RE
    Replies: 7
    Last Post: 11-04-2007, 07:45 AM
  5. old frick system monitor
    By rasgrant in forum NH3
    Replies: 5
    Last Post: 17-01-2007, 07:15 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •