    Shell/Tube flow rate?



    Can anyone tell me if there is a rule of thumb calculation for water flow rates through shell and tube evaporators?
    Obviously depending on the application the water pump will be be designed for an appropiate head but what about the minimum litres/sec flow rate in comparison to the tonnage rating of the heat exchanger??



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51
    Hi Reggie

    just use the proper formula Q = m c delta t

    where

    Q = refrigerating effect of the evaporator in kw

    m = mass flow of water in kg/s (sorry, couldn't get the dot above the m)

    c = specific enthalpy of the fluid in kj/kg (for water it's 4.19)

    delta t = difference in entering and leaving water temperature (C)

    so to find the flow rate of water through the exaporator you will need to know the refrigerating duty of the evaporator and then transpose the formula thus

    m = Q/c x delta t.

    if your evaporator is rated at, say, 80kw and your entering water temperature is, say,12C and the leaving temperature is, say, 6C then the water flow required would be

    80/4.19 x (12 - 6) = 3.182kg/s or l/s

    you could also use Q = m x delta h from the Mollier chart

    hope this helps

    Frank
    Last edited by frank; 02-11-2002 at 03:55 PM.

  3. #3
    Join Date
    Apr 2001
    Location
    The Netherlands
    Age
    63
    Posts
    51
    Rep Power
    24
    Don't forget the limitations Reggie. Limitations for minimum flow when running at critical conditions like evaporation below freezing point and maximum flow causing turbulent flow and after a while causing leakage. Depends also whether the refrigerant is in the tubes or the water.
    Condensers are sensitive for minimum flow as well due to scaling and biological growth.
    Nico.

  4. #4
    Join Date
    Mar 2001
    Location
    Derby, England
    Age
    57
    Posts
    86
    Rep Power
    24
    Oh Frank

    You're such a knowledgable bas*ard! Hee-Hee

    Mr Frosty

    PS - you wouldn't have happened to have been to college for approx 2.5 years would you? LOL

    See you soon, Franky Boy

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51
    Mr Frosty

    How nice it is to see you back on the forum - what's up? is the fishing season over? - put the bike away for the winter have we?

    You can't beat the basic's mate - they work every time! - why don't you copy my previous post and teach it to your students they might learn something for once

    Give me a ring if you need me to explain it to you!

    Frank

Similar Threads

  1. flow switch connection
    By afeef in forum The Trail of Tears
    Replies: 18
    Last Post: 23-12-2009, 06:55 PM
  2. R-134 Chilling Unit
    By enginerous in forum Industrial
    Replies: 32
    Last Post: 25-08-2002, 01:12 PM
  3. Accidental Release Flow Rates
    By mbeychok in forum Commercial
    Replies: 0
    Last Post: 20-11-2001, 01:52 AM
  4. Accidental Release Flow Rates
    By mbeychok in forum Industrial
    Replies: 0
    Last Post: 20-11-2001, 12:53 AM
  5. Accidental Release Flow Rates
    By mbeychok in forum Tools and Calculators
    Replies: 0
    Last Post: 20-11-2001, 12:45 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •