Results 1 to 12 of 12
  1. #1
    Join Date
    Jul 2007
    Location
    malaysia
    Posts
    15
    Rep Power
    0

    how to calculate weight of refrigerant



    i hav a coolroom system . so how to calculate the system need how many weight of refrigerant ?



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Age
    55
    Posts
    53
    Rep Power
    18

    Re: how to calculate weight of refrigerant

    You need to know what state the refrigerant is in at individual parts of the system IE gas or liquid,then calculate the volumes of each component based on the density of the refrigerant.For example suction line volume & gas density at expected suction temperature or pressure from the refrigerant tables should give you KG/M cubed.Do this for all components and you have an estimate of charge.Be careful with mixed fractions of refrigerant.Once you have an estimate you can charge the unit and adjust as needed for the system application.Don't be surprised if its different though.
    Hope this helps.

  3. #3
    Join Date
    Jul 2007
    Location
    malaysia
    Posts
    15
    Rep Power
    0

    Re: how to calculate weight of refrigerant

    if i want learn this , where can i find the information is about this ?

  4. #4
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: how to calculate weight of refrigerant

    Quote Originally Posted by steven86 View Post
    if i want learn this , where can i find the information is about this ?
    From all that I have learn't dont bother trying to gues it, just charge the system via super heat and sub cooling then jot down what it took, this seems to be the best most effective methode.

    But non the less I may be wrong, but thats what I have picked up so far from the guys on this board and from the local techs here that I've worked with.

  5. #5
    Join Date
    Feb 2007
    Location
    United Kingdom
    Age
    45
    Posts
    48
    Rep Power
    0

    Re: how to calculate weight of refrigerant

    Quote Originally Posted by The MG Pony View Post
    From all that I have learn't dont bother trying to gues it, just charge the system via super heat and sub cooling then jot down what it took, this seems to be the best most effective methode.

    But non the less I may be wrong, but thats what I have picked up so far from the guys on this board and from the local techs here that I've worked with.
    I would agree with MG above.

    Never charge a system based solely on estimated refrigerant weight. Always base it on the superheat, subcool, dry bulb and wet bulb temperatures and the temperatures of the various pipes.

    If you weigh the amount of refrigerant you put in, you will then know how much you have charged.

  6. #6
    Join Date
    Oct 2005
    Location
    nottingham UK
    Posts
    109
    Rep Power
    19

    Re: how to calculate weight of refrigerant

    we were always told to keep an eye on a clamp meter checking compressor run current when charging a system as well

  7. #7
    aoehero's Avatar
    aoehero Guest

    Re: how to calculate weight of refrigerant

    Can you use the weight of the cylinder to do your initial OZ input?

  8. #8
    Join Date
    May 2006
    Location
    Bristol
    Age
    51
    Posts
    4
    Rep Power
    0

    Re: how to calculate weight of refrigerant

    I am in total agreement with Davej. Ive been taught by my 'old school' boss & if you have no design information to go on or you are retrofitting then charge as per running amps of the compressor, assuming the compressor is new. Obviously bomb charge the system with a base charge usually just before gauge/system pressure equalises then switch on & monitor running amps.

    Then you can verify with superheat measurements and air on air off both heat exchangers comparing against room temp. I would always do this over charging a system to full sight glass as this often masks fault conditions at the expansion valve . Then document all findings & label unit with commissioning sheet.

  9. #9
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: how to calculate weight of refrigerant

    Quote Originally Posted by aoehero View Post
    Can you use the weight of the cylinder to do your initial OZ input?
    If you want to but it is a very strange question
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  10. #10
    aoehero's Avatar
    aoehero Guest

    Re: how to calculate weight of refrigerant

    most all liturature will say something like 260 oz +/- something. Why give a measureable figure if noone uses it?

  11. #11
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: how to calculate weight of refrigerant

    Quote Originally Posted by aoehero View Post
    most all liturature will say something like 260 oz +/- something. Why give a measureable figure if noone uses it?
    And how does this relate to your question about the cylinder tare weight inclusion?

    260oz for what? A total charge or a top-up, what does this refer to?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  12. #12
    Join Date
    Sep 2007
    Location
    Belgium
    Posts
    14
    Rep Power
    0

    Re: how to calculate weight of refrigerant

    The only way to know exactly the required refrigerant charge is with a void fraction model applied to the evaporator and to the condenser...
    It can of course be evaluated by making rough hypotheses...

Similar Threads

  1. R600 Refrigerant.
    By tonydeith in forum Refrigerants
    Replies: 14
    Last Post: 21-04-2011, 08:52 AM
  2. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 12:39 PM
  3. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM
  4. Replies: 4
    Last Post: 31-01-2004, 08:16 AM
  5. Refrigerant Reclamation
    By herefishy in forum Commercial
    Replies: 6
    Last Post: 23-07-2003, 08:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •